11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
3 line PT's prot./meter in 11kv side(before side)
3 prot/meter. CT's at 11kv side(before side)
3 line PT's prot./meter in .433kv side(after side)
3 prot/meter. CT's at .433kv side(afterside)
In each CTs & PTs,ther wil b a seperate core for metering n
protection,dont get confused with the windings in assuming
tat this is for ef,oc and differential,get a CT/PT wit both
metering n protection whatevr d core is depends upon our
application in relays.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / manax
transformer primary side one set (3 nos) ct,pt and
secondary side one set ct,pt required.each ct pt consist 2
core one for metering,one for protection.this LT
Transformer so no need any special protection.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / a.k.mishra
3 ct having 3 core for metering & protection
3 pt for mounted R,Y,B induvisualy for metering & protection
also 1 neotral ct is requried for star connection
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / jesudoss
transformer secondary (433v)-3 ct for over current
-1 ct for restrictedearthfault.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / vishal
3 CT's and 3 PT's wil; be required for each phase of transformer
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / d.k.sahu
At primary side 3 nos ct for metering & protection,1 no
cbct & 3nos pt.
At secondary side 3nos ct & 3nos pt.
Total ct/pt : 13no
| Is This Answer Correct ? | 0 Yes | 0 No |
Can any body explain the operation system of MVWS(May be related to water and fire hydraunt system)?
what will be happen if earth point is being used for as a neutral point for raw power , and same will be used for ups earthing
what is the use of spst switch in performing experiment on self excited dc motor?
what are factors comes under relay setting (distance relay 7sa52) under OPEN DELTA VTs connection??
What are the maximum and minimum ratings of MCB,MCCB,ACB,OCB,VCB and SF6 breakers?
2 Answers ABB, SK E&C, Sodexo,
In LT Line What is the minimum clearance required between phase to phase busbar & between Phase to body of the panel? Also between Neutral &phase, & Neutral & body of panel. as per standards.
Can earth resistance be measured without connecting the earth electrode? and should earthing connections be disconnected What is the effect of connecting two cables of different sizes in parallel with supply? Thanks in Advance. I am intrested to get in touch with some tecnocrats/engineers,my mail i.d is : hiremathvijay@rediffmail.com
125Kva Dg can take up how much amphere load.
We have a 33/11kv switchyard having 12.5 MVA power transformer. We export & import power through this transformer. When we export power, the PF will be depend on GRID PF & when we import power the PF will be depend on our load PF. but the problem is that,when neither we export nor import but our 33KV vCB is in close position,our meter read the power factor 0.14 to 0.25 at that moment. So how can be we improve the power factor at that moment.
why DC is not generated instead of AC?
Do these factors (settling time, peak time, steady state error, overshoot, rise time, MPOS (Maximum percent over shoot)) are the part of first order, second order, higher order, linear, non-linear, open-loop, closed-loop, homogeneous & non-homogeneous systems ?
What type of fittings and electrical accessories can be install in radiation area ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)