11kv/0.433kv, 2 mva , transformer , for protection and
metering how many CT/PT are required?
Answers were Sorted based on User's Feedback
Answer / shailesh taware
1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING
Is This Answer Correct ? | 10 Yes | 3 No |
Answer / manjunath kunigal
one set of tertiary winding CT/PT is sufficient for both
metering and protection.
Is This Answer Correct ? | 11 Yes | 9 No |
Answer / k n naidu
hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mubanga mulenga
You need:
1)Inst., o/c, Metering & EF - 3 CT's
2) REF - 1 CT
3)SBEF - 1 CT
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vikas chauhan
3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / d ramesh
11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.
0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.
1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.
panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.
Is This Answer Correct ? | 2 Yes | 1 No |
why high voltage is reqiured or L.T. panels? what type of tests should be taken for electrical panels?
where to use 3.5 core and 4 core cables, will this vary for type of loads
How to design the earth grid for lightning protection in an industry
What happen if 200 KVAR capacitor connected to power continuesly?
What is Bolted fault?
What is the formula for finding fault level of generator?
i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?
HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION
on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help
what is the function of RMU?
what is relation between voltage and current and don't take resistance here. if we supose say when there is increase in voltage whwt happens to current?is it decrease or increase?
Hod do u calculate cable size for underground laying and the factors effecting/influencing it??