11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / shailesh taware

1 CT WITH 3 CORE
1st CORE FOR O/C & E/F PROTECTION
2nd CORE FOR METERING WITH INSULATION CLASS 0.5
3rd CORE FOR DIFFERENTIAL PROTECTION
1 PT WITH 2 CORE
1st CORE FORE O/C & E/F PROTECTION
2nd CORE FORE METERING

Is This Answer Correct ?    10 Yes 3 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / rakesh

3 ct for metering ,3 ct for protection,3 pt

Is This Answer Correct ?    11 Yes 6 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / priyadharisini

3 nos of CT/PT required

Is This Answer Correct ?    6 Yes 3 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / manjunath kunigal

one set of tertiary winding CT/PT is sufficient for both
metering and protection.

Is This Answer Correct ?    11 Yes 9 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / sandeep

3 CT/1 PT

Is This Answer Correct ?    5 Yes 4 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / senthil kumar

06CT and 03PT'S

Is This Answer Correct ?    3 Yes 2 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / k n naidu

hi,
one three phase set of PTs for both protection & metering
and one three phase set of CTs with two secondary cores one
for metering and protection are required.

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / mubanga mulenga

You need:

1)Inst., o/c, Metering & EF - 3 CT's

2) REF - 1 CT

3)SBEF - 1 CT

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / vikas chauhan

3 no CT (Double core) for 11 kv side for protection and
metering
3 no CT (Double core) for 0.433 kv side for protection and
metering
11/.110 KV 3 phase PT for 11 KV side
secondry side(.433KV side) phase directly connected for
Metering & select relays for .433 KV secondry voltage.
if you select differencial rotection
3 nos CT for Primary and 3 No CT for Secondry side and
interposing CT for Match and neutralise the current in
relay.

Is This Answer Correct ?    1 Yes 0 No

11kv/0.433kv, 2 mva , transformer , for protection and metering how many CT/PT are required?..

Answer / d ramesh

11KV side(delta)
Line side 3core CT :1No. for metering, O/C&E/F protection,
Differential protection with ICT.

0.433KV(Star)
Nuetral CTs :1core for Standby E/F 5p20
Line CTs :3core CT:1No for metering, O/C&E/F
protection,Differential protection with ICT.

1No. 1-core CT in LV nuetral of Transformer of class 5P20
for earth fault protection.

panel side in the panel itself remaining CTs can be
provided for metering, O/C&E/F, and differential cores with
ICT. In both HV panel & LV panel.

Is This Answer Correct ?    2 Yes 1 No

Post New Answer

More Electrical Engineering Interview Questions

why high voltage is reqiured or L.T. panels? what type of tests should be taken for electrical panels?

2 Answers  


where to use 3.5 core and 4 core cables, will this vary for type of loads

1 Answers   KSBC, Medreich,


How to design the earth grid for lightning protection in an industry

2 Answers  


What happen if 200 KVAR capacitor connected to power continuesly?

0 Answers  


What is Bolted fault?

0 Answers  






What is the formula for finding fault level of generator?

11 Answers  


i want to learn control schedule for 11kv panel? can any one send the detailed control schedule?

0 Answers  


HOW TO CALCULATE CAPACITOR BANK OR HARMONIC FILTER CALCULATION

0 Answers   ECCI, EFS,


on a three-winding transformer relationship delta-delta-star, on third winding why the relationship is a star? what are the advantages and disadvantages? Thank you and please help

0 Answers  


what is the function of RMU?

4 Answers  


what is relation between voltage and current and don't take resistance here. if we supose say when there is increase in voltage whwt happens to current?is it decrease or increase?

4 Answers  


Hod do u calculate cable size for underground laying and the factors effecting/influencing it??

4 Answers   Kuwait Oil Company,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)