i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.
Answers were Sorted based on User's Feedback
Answer / vinit patil
You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / a k kataria
Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishna chaitanya
first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b2
Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B
| Is This Answer Correct ? | 1 Yes | 8 No |
what is potentiometer & rheostat
what is the transformer
Difference between earthing & grounding.?
can we calculate the diameter of the cable by its cross section?
Power Factor Controller
What is transister , thermister , thyrister? what is its function? where this using?
Control cables in S's will carry 1000v which is AC R DC? Pls answer me
How conventional fire alarm system works?
which motor is used in watch..??????
Generator protection &generator test
what is ten delta ?
WHICH IS BETTER( FOR POWER SAVING)- ON LINE OR OFF LINE UPS ?
3 Answers Punjab National Bank,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)