Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.

Answers were Sorted based on User's Feedback



i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / vinit patil

You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.

Is This Answer Correct ?    5 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / a k kataria

Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.

Is This Answer Correct ?    2 Yes 1 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / krishna chaitanya

first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com

Is This Answer Correct ?    1 Yes 2 No

i have one transformer 1000kva, 11/.433kv. we are using 200/5 amp. ct unit for measuring purpose, ..

Answer / b2

Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B

Is This Answer Correct ?    1 Yes 8 No

Post New Answer

More Electrical Engineering Interview Questions

if the magnetic lines can pass through a vaccuum area

0 Answers  


what is the difference between skin effect

0 Answers  


What do you understand by avr?

0 Answers  


Based on CPI/CGPA they shortlist the candidates & than directly start Interview so there is no Written Exam or GD Only PI.Interview held @ MNNIT , ALLAHABAD On-Campus on 6th,Aug, 2007 & the Questions asked to me by Interview Board ( 4 People) are from HR/SummerTraining/BTP/Subject-core, POWER SYSTEM & MACHINE. time duration of I/V is about 15-20 Minutes. HR- Q.1 Name,hobbies & About family background ? Q2.What u know abt NTPC ?? Q3.Why u want to choose NTPC as ur Carrier's starting i.e power sector not any other Oragnisation or sector ?? Techincal Questions- Q1.What is the reason for transformer Noise ?? Q2.Which material is used for making Transformer oil & How u measure its dielectric strength & Name the test ? Q.3 Which Machine u will prefer 2 use if flammble gases are coming out at a place & why ?? Q4.What is relation b/w Transmission Lines & Communication Lines ? Q5.What is the maximum capacity Synchronus Machine & total powerGeneration in our country ? Q.6 In india Power generation is at 50Hz while in America its 60 hz ,why so ?? Advantage or disadvantage ?? Q.7 Maximum Generation Voltage in india ? Q8. What is the Voltage regulation & why its required n how much is permissible ? & causes of voltage variation ?? Q.9 Why electric shock is feel ?? n in a Electric Train why we didnt feel that ? Q.10 Have u seen/ experience of any power plant/ industry related to the power sector ? so these are the questions which not too diffcult i think was asked to me.

6 Answers   NTPC,


1.what is electricity 2.what is electronice 3.how many modules 4.five electrical component with symbol 5.five electronice componene with symbol 6.how convert 220v.A/C to 24v/DC 7.220V.WAIRING DIAGRAM OF AMMETER/VOLTMETER/OHMMETEER

1 Answers   Hatsun,


A 11 KV motor is working. if the supplay is fail. what will happened with it's breaker? Trip / remain the same condition?

4 Answers  


Is there any reason that we get shock on touching phase wire because the earth is at neutral potential? Is there any reason that the earth is at neutral potential because the neutral is earthed in apower station

0 Answers  


how to erect roof control panel?

0 Answers  


How do performance buccholz relay testing in power transformer

1 Answers  


which is the most advanced form of SF6 BREAKER?Can we use other gases to quench the arc?

0 Answers   TATA,


Why the Transformer Nuetral is grounded?

10 Answers   Infosys, Khartoum Refinery,


what will happen if phases are not shorted with neutral in transformer impedance test? and if neutral is not connected with ground?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)