i have one transformer 1000kva, 11/.433kv. we are using
200/5 amp. ct unit for measuring purpose, & one 800 amp.
V.C.B Unit for the same t/f operate, i wants to known the primary
current of T/F is only 53 amp. why we used 800 amp.
V.C.B ? & 200/5 amp. CT Unit.
Answers were Sorted based on User's Feedback
Answer / vinit patil
You are right, you should fight with your electricity board
regarding the HT Metering CT ratio. You should actually
required 100/5 ratio.
But while deasigning VCB it is always prfarable to go on
higher side because it can sustain the heavy short circuit
current. One thing should be noticed that the protection
CTs should be as per the Primary current of the ransformer.
| Is This Answer Correct ? | 5 Yes | 2 No |
Answer / a k kataria
Well given the rating of transformer as 1000 kva, CT ratio
should have been 100/5. As far as VCB current rating is
concernd,these are generally made for universal
applications and are generally 630 Amps onwards 'cause in
the eventuility of fault ,heavy currents are to be taken
care of.More over increase in the rated current capacity of
breaker adds little to the cost compared to other
components of the breaker.There fore capacity of VCB is OK.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / krishna chaitanya
first u must know that transformer transforms with
no change in power. As its 11 kv on primary side as
per funda you can calculate primary current 53 amps.
P = vi cos fi. A 100/5 ratio ct is enough to measure.
But its always advisable to select equipments with
larger than required ratings. Sometimes u'l see a
300/5 ratio ct.
and vcb, 800 amp vcb is for load. There'l be another
breaker at secondary of transformer with larger than
this amp rating. 800 vcb is provided for a particular
load control.
checkchaitu@yahoo.com
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / b2
Transformar steap down the voltage so current grow up high
so we are use 200/5 amp. ct & 800 amp.V.C.B
| Is This Answer Correct ? | 1 Yes | 8 No |
What is Earth Fault and Over current Fault.
a governer in an Ic engine controls the
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
why we used to transmitt the power at higher voltage why not at lower voltage
What is application of isolation transformer & How it works.
what are the C&D CHECK OF DG set
Explain RLC circuit?
what is buffer resistance starter.?.What is the working principle and where it is used..?
what the main difference of the 3 phase and 2 phase power supply??
What is meant by sag?
What is meant by harmonic distortion?
How can we convert dc to equivalent ac??
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)