For 150 mtr cable run from DCS panel to transmitter (24 VDC with 4-20 ma output), need cable size. 1.5 sqmm is suitable?
Answers were Sorted based on User's Feedback
Answer / mugil
below 250 mtr you can use 1.5 sqmm and above 250 you should use 2.5 sqmm.Because if length is increasing voltage drop will increase that is the reason we are increasing cable the core size.
Is This Answer Correct ? | 10 Yes | 2 No |
What is the difference between a Extension cable and a copnesating cable.Where can we use compensating cable. Is anywhere compensating cable are used for mv transmission to the indicator.
In s7-200 we use HMI TD-200C , what that C stands for........ plz reply
how to define the P,I,D value in tuning pid loops in online.
Sir, my yokugava FF TYPE LEVEL transmitter us bad, i don't have spares available, i want to replace it with a Rosemount FF transmitter, please tell me what procedure to be followed and what changes to be done in dcs part.
1 Answers BPCL Bharat Petroleum, OEG,
What is the expansion of RADAR? How it works?
how 3 out of 2 Logic/interlocks works? give brief explanation with help of diagram.
can i calibrate DP transmitter online (while Tx in Service) if yes ,how?
what is the difference between Ethernet unmanaged and managed Switch?
A pressure differential gauge type of instrument has a manifold with 2 isolation valves (hp and lp),2 vents(1 each for hp and lp) and 1 equalizing valve. Determine the position of each valve(either fully closed or fully open) when troboulshooting to: 1. zero the transmitter. 2. determine if there is a block in the impulse line. 3. determine if the gauge is functioning properly. The process fluid is water.
Explain Gas Turbine startup and shutdown sequences
How LVDT position transmitter works on DC supply(24vdc) from DCS, whereas transformer operates on AC supply? pls help..
In Boiler Drum Level- Level control valve how can it tuning (PID)?