Answer / carl_ellis
In order to 'wet'calibrate a transmitter (by applying
reference pressure), the transmitter needs to be powered,
but if the transmitter's output signal is an input to a
control loop or alarm, then those functions need to be
disabled (loop put in manual, alarm disabled) because the
transmitter's output is not representative of the process
during calibration.
The transmitter has to be isolated from the process, so that
cal pressure can be applied. This done through isolation
valving; typically a 3 or 5 valve manifold for a DP transmitter.
So, is a transmitter 'in service' if it's powered, but its
signal is not representative of the process and is, in fact,
isolated from the process?
My answer is no, a transmitter being calibrated is not 'in
service'.
Carl Ellis
Measure First
Is This Answer Correct ? | 3 Yes | 0 No |
why the steam drum and deaerator level transmitter range is in negative MMWC to zero
3 Answers Emerson, Jindal, JKPM,
what type problems create in radar level transmeter and what is its solution
what is commisioning procedure,2)what is is the main work in commisioning in the field tx to dcs, plz send me detail
How to adjust the zero & span of a control valve from the posiitioner(MIL)?
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
why we use the ac supply load cell>?can we use the dc supply load cell?advantages and disadvantage of the ac supply load cell?
what is beta ratio?
how to calculate temp.prapotional to mv in thermocoulpe.
what is difference between OP AMP and differential amplifier?
How oil line flow measured?eplain about instruments used and working principle?
3element
How do understand by hart protocol?
4 Answers BW Instrumentation Electrical,