Answer / carl_ellis
In order to 'wet'calibrate a transmitter (by applying
reference pressure), the transmitter needs to be powered,
but if the transmitter's output signal is an input to a
control loop or alarm, then those functions need to be
disabled (loop put in manual, alarm disabled) because the
transmitter's output is not representative of the process
during calibration.
The transmitter has to be isolated from the process, so that
cal pressure can be applied. This done through isolation
valving; typically a 3 or 5 valve manifold for a DP transmitter.
So, is a transmitter 'in service' if it's powered, but its
signal is not representative of the process and is, in fact,
isolated from the process?
My answer is no, a transmitter being calibrated is not 'in
service'.
Carl Ellis
Measure First
| Is This Answer Correct ? | 3 Yes | 0 No |
hi friends,im an instrumentation and contol engg student,can u hlp me of suggsting barc written question paper,my id is roysuvaranjan@gmail.com, cel no.9563591747
How do we MEASURE OR CALCULATE VELOCITY used to calculate REYNOLDS NUMBER??
why Fahrenheit unit of moistur analyzer transmitter
what is instrument termination
What is the difference between Pressure Safety Valve and Pressure Relieve Valve, in what condition we prefer choose Pressure Safety Valve rather than Pressure Relieve Valve? and vice versa
I have energy meter for educational project having 0.5s class but my friend need 0.2s class meter , which one is good for that purpose and what is the actual difference of that two classes , need very easy example also.??
Advantages of servers over normal desktop in PLC SCADA system
Pl send the model question paper of mahagenco account officer post
Is there is a device to convert mechanical energy to electrical energy
If you SOURCE your outputs from a PLC, would you have to make the output HIGH, or LOW, in order to switch an output ON?
how to trim the pressure transmitter ?
What is cavitation. what is the effect of it on control valve and how is it prevented.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)