What is the solution if rotork motorised control valve showing pink Colour in dcs.

Answers were Sorted based on User's Feedback



What is the solution if rotork motorised control valve showing pink Colour in dcs...

Answer / aswin

This pink colour seems that valve is in between condition.So we have to check the position of valve open and limit switch switch not acted or physically valve is in middle position.

Is This Answer Correct ?    1 Yes 1 No

What is the solution if rotork motorised control valve showing pink Colour in dcs...

Answer / elheiven

Up the torque limit then power cycle if the motor stalled is not working try to change main power pcb or power module

Is This Answer Correct ?    0 Yes 0 No

What is the solution if rotork motorised control valve showing pink Colour in dcs...

Answer / ejaz

Check the local display in the MOV. If valve have any issue it will show the exact error. for example MOTOR STALLED. MOTOR STOPPED. first check the phasically status on the local display

Is This Answer Correct ?    0 Yes 2 No

Post New Answer

More Instrumentation Interview Questions

what are the types of a thermocouple

2 Answers  


How can I map a tank?  Tank 15m h and 42m dia. we just fixed radar type lit. its reading shows over range. Now its required mapping ?

1 Answers   CMC,


How to Calibrate Radar Level Transmitter in Field

0 Answers  


Galvanizing.

0 Answers   CCIE,


what happen if i increase height of displacer type LT.accuracy or sensitivity are affected.why?

0 Answers   Essar,






How can I zero check of wet leg type DP Tx ?

6 Answers   ONGC,


Q1: Consider part of a control loop, which excludes the transmitter, consisting of a process, a controller and a control valve which may be represented by two dead times of 0.5 min each and three exponential lags of 0.8 min., 1.0 min. and 1.5 min. respectively. We wish to express this system as an overall first order plus dead time (FOPLD) model ie gain, time constant and process dead time. (We will see later that this is often done, to simplify controller tuning). For this exercise, gain is considered to be 1.0. (A) If the transmitter is a flow transmitter whose behaviour can be described by a dead time of 0.2 min. and an exponential lag of 0.5 min. in terms of the overall dead time and overall first order lag how can the system behaviour be approximated ? Overall dead time = Overall time constant = (B) If the transmitter is a temperature transmitter with a temperature sensor in a protecting well whose behaviour can be described by a dead time of 0.7 min. and an exponential lag of 15 min. how can the overall system behaviour be approximated now? Overall dead time = Overall time constant =

0 Answers  


What is the meaning of wet leg

0 Answers  


How many mode are in ups?

2 Answers  


what is the calibration procedure for magnetic flow meter @ onsite

0 Answers  


Conversions

0 Answers   CCIE, Nestle,


what should be distance from tapping point to inallation place of instruments?

3 Answers   Tasnee Petrochemicals,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)