we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
Answer / chanchal
at first check the air supply.if it is ok then
feed the 4mA by using calibrator in i/p converter of positioner. if valve is zero position(fully closed) then its ok.if valve is not in zero position(fully closed) then set the zero position in positioner by using zero point screw.
next feed the 20mA by using calibrator in i/p converter of positioner.if valve is 100% open then its ok.if valve is not 100% open. then adjust the span setting by using span screwin positioner.
then check 25%,50%,and 75% open position in valve by feeding 8mA,12mA,and 16mA by using calibrator in same way.
| Is This Answer Correct ? | 4 Yes | 5 No |
Why do we have earthing cable in branch cable and shield in the same cable?
0 Answers Process Control Technologies,
wt kind of business we can do by usig PLC?
Calibration procedure for electro magnetic flow meter
Working principle capacitance type level transmitter
protection relay watchdog contact operation?
Explain the functions of the CPU of a PLC.
how to check thermocouple ,its working or not?
14 Answers Coca Cola, Ford, Honeywell,
how we can calibrate an Interface level transmitter online
how can i check vortex shedder bar it is ok? if there is ohms condition are shown correct?
Thermocouples work as follow:
1 Answers Dashen Brewery, Tata Power,
1.what is the effect of vapour presuure in orifice plate flow measurement 2.which is more effective 2 pressure sensors or one single differential pressure sensor in orifice plate measurement 3.how to design a v/i converter and i/v converter 4.how many type of thermocouple are there 5.how many leads are there in thermocouple measurement 6.how pressure sensors are connected in level measurement in differential pressure method 7.what is the output of capacitive pressure sensor (ac or dc),how its o/p is signal charactarized 8.what is the physical meaning of discharge coeeficient,why it is calculated,orifice plate what is its value,why it is less than 1,Q at upstream is equal to or not equal to Q at downstream of orifice plate why?what is vena contracta in orifice plate 9.why rotameter is called variable area flowmeter,it can measure flow even if area is not varying,why it is made tapered 10.design a 10 bit counter ,which counter you will prefer 11.how to remove self heating error in RTD 12.which is more sensitive pt100 or pt50 13.why thermocouple are connected in parallel 14.what is lead contact error in RTD,how to avoid 15.what is P,PI,PID,PD controller,why there is no ID controller 16.what is override,split range,sequential,ratio,feedforward,cascade controller 17.why we moved from SR to JK and then JK to master slave JK flipflop,give correct reason 18.how to measure level of a closed container which contains vapour and liquid,remember no vapour gas should be leaked,so ultrasonic and capacitive is not an option,design another method 19.how to design horse race counter including sensors and signal conditioning element 20.what is bevelling
how to work MIL contol valve posistioner ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)