Please anyone answer my question, what is the difference
between single acting and double acting control valve, in
what condition we better choose single acting rather than
double acting
Answers were Sorted based on User's Feedback
Normally a control valve is refer to by it's fail position.
This means "what position will the valve move to should the
supply air or control signal to the valve falls away". This
is important to safe guard the process at various places so
some valves will be fail open and some fail close. In order
to have valve as a fail open or close the valve the actuator
have to be spring loaded. So by having the spring on top or
bottom of the actuator piston, will determine if it will be
a FO or FC valve. This kind of valve is also called single
action since it will only have one output from its
positioner to either the top or bottom of the actuator. The
positioner on the valve is also setup as a single acting
positioner since it will only give a single action to the
actuator, the reverse action will be done by the spring. The
problem with this setup is that it is possible that the
process might be so strong or the pressure so high (during a
blow down or ESD shutdown in the plant) that the spring
might in certain instances be to week to push the valve into
the fail position quick enough, due to the back pressure
from the process and can cause damage to the plant or even a
explosion. To make sure that the valve will go to the fail
position we install a double action positioner with two
outputs. One goes to the top of the actuator and one to the
bottom. This is also very helpful to do very accurate and
stable control on a high flow line since the pressure from
the position do the actual control and not spring control
one way and positioner control the other way as in single
acting control valves. It is also solving the problem that
the valve will now be forced into the fail position by the
spring as well as the positioner supply pressure during a
emergency.
In shutdown valves (open/close ESDV's) the same is true and
sometime at critical and high pressure points we use
hydraulics instead of pneumatics as the double acting agent
to make sure the valve will close during a emergency.
So to summarize the double acting action in ESD and control
valve is just there to make sure the valve will do what it
was designed for. Call it a extra fail safe if you want. In
theory not needed since a single acting valve should do the
trick just as well,but in practice you are at time very glad
you did it especially if you look at the kind of pressures
the valves are working on. With those kind of flows and
pressures you don't want to leave anything to chance.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / b.c.bhatt
Basically single acting valves returns to their original
position as the control input goes off. These can have NO
or NC positions depending upon the application .In double
acting valves or bistable valves ,the position is retained
even when control input is withdrawn.
| Is This Answer Correct ? | 2 Yes | 0 No |
what is working principle of vibration prob
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
why we are not using the turbine flow meter in the steam service?
What is the meaning of Feedback? How many types it is? Explain it?
How much should be the values and/or percentages of these given below factors for a good controller ? Steady state error Delay Rise Time Overshoot Peak Time Settling Time Damping Oscillations & vibrations thanks
What is super thermocoupal?
what is proportional & what is proportional band
Why would an Engineer consider combining FEEDBACK and FEEDFORWARD control in some applications?
If I installed wrong directions orifice plate then what showing value d.p transmitter?
what is solenoid valve?
why we set -10 volt in vibration sensor output,why not +10 volt
Lux meter is the measuring device to measure the lux level of lighting fixture. in industrial sector two types of lighting fixture is being used as street lighting purpose 1. HPSV (Sodium) and 2. HPMV (Mercury). HPMV having white light which is an combination of red, blue and yellow colour, while HPSV haivng Yellow lighting. in HPSV red & blue colour will be absent. during measurement of the lux level of HPSV and HPMV fixture. 1. Lux meter can measure the actual lux level of both fixture? 2. or it will show false reading for HPSV fixture light as it has only yellow light present. please give me answer
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)