How to calculate incoming cable size for 33KV, 1MVA transformer.
Answer / ak
calculate line current for transformer
I=1000000/(1.732 x 33000)
=17.50 Amps
based on the value of current select appropriate cross section area of particular gauge.
Is This Answer Correct ? | 6 Yes | 1 No |