When alarm is activated in buccholz relay in transformer
Answer / spl
Depending on the model, the relay has multiple methods to detect a failing transformer. On a slow accumulation of gas, due perhaps to slight overload, gas produced by decomposition of insulating oil accumulates in the top of the relay and forces the oil level down. A float switch in the relay is used to initiate an alarm signal. Depending on design, a second float may also serve to detect slow oil leaks.
If an arc forms, gas accumulation is rapid, and oil flows rapidly into the conservator. This flow of oil operates a switch attached to a vane located in the path of the moving oil. This switch normally will operate a circuit breaker to isolate the apparatus before the fault causes additional damage. Buchholz relays have a test port to allow the accumulated gas to be withdrawn for testing. Flammable gas found in the relay indicates some internal fault such as overheating or arcing, whereas air found in the relay may only indicate low oil level or a leak.
Is This Answer Correct ? | 3 Yes | 0 No |
WHY FEEDERS TRIP IN COLD AND FOGY WEATHER?
Can a transformer designed for a particular voltage and frequency rating be used for different set of mentioned ratings? Assume that the winding does not get burnt because of overheating at higher voltage. If yes, then under which constraint it is possible?
What is the most accurate way of testing ELCB?ELCB is better than RCD?
how does commutator convert a.c to d.c?
0 Answers NRSC National Remote Sensing Centre, RBC,
What is mean by sinewave.
What is auto transformer?
28 Answers ABC, Transformers and Electricals, US Consulate,
definition of transformer
Can we connect CBCT in the Busduct
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
What size cable is used for HT cable to the transformer of 630kVA, and the supply voltage is 11kV
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
Sir if i have 2kv ups in which 17ah 8 battries load 600watts how much back up time i get and if i put 6kv ups with the same no of battries same amp can i get more back up time please give reply exactly what is the procedure to calculate back up time for different kv,s