in one substation we have two power transformers of
100mva,75mva capacity.statoin load is155mva.how much each
tranformers share the load????
Answers were Sorted based on User's Feedback
Answer / tara shankar gupta
Any system desined is to optimam utilisation,here we have
to Xmr ie 100 MVA and 75 MVA, connected load is 155 MVA in
this case we cant optimize 75 MVA Xmr. in such situations i
will suggest Maximam loading of Big Xme and Load rest MVA
to smaller one.
| Is This Answer Correct ? | 5 Yes | 0 No |
Answer / asm
first you have to confirm that 155MVA is connected or
diversified load, if it is connected load then 90% loading
is coming. however if it is diversified load then u can
load upto 80% of transformer capacity. in this case X'mer
will be out of higher efficiency range.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / santhosh
both the transformer is same rating it would be share equal
load,i.e (trafo1=2000kva,trafo2=2000kva),current load is
2200kva, now trafo1=1100,trafo2=1100
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.prakashchandra
The voltage drops in the transformers + line should be equal
at the secondary bus-bar. Current shared by tr1 x its %
impedance = load shared by tr2 x its % impedance.Hence The
load sharing ratio is inverse to ratio of % impedances.
| Is This Answer Correct ? | 1 Yes | 0 No |
The load sharing will be in the inverse ratio of percentage
impedances. Lower the % impedance higher the load ,so that
the voltage drops are equal. .
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / harry
Higher Value Transformer u can Load upto 90% say 90MVA &
Lower Value Transformer u can load Load the Rest Say
remaining 10MVA.
It is General Practice to Do the Distribution of Load
According to above said manner
| Is This Answer Correct ? | 1 Yes | 8 No |
how to calculate the magnetizing current of ct ( 800A/1A) for Relay 64
what reactive how to maintain
how we can know which is Lv side and HV side of transformer by just seeing it?
How is the speed of a DC shunt motor related to the armature current?
what is difference between 2 pole structure and 4 pole structure in transformer yard
Why the earth cable have current 1A - 2A , it is safety for Electrical system or earth cable should be zero amps ? how to troubleshoot?
How the earth fault relay works please explain?????????
Sir, I completed DEEE... And now I working in TNEB for one year apprenticeship. If I eligible for applying c license and how can I get?
11kv has three live wires how much voltage is in its single wire(leaving the other two wires)
1)Explain why the cradle guard is used on railway crossing in overhead line construction?
What is mean by CT Saturate? how do we calculate?
I need to calculate the Battery bank back up for below configuration:- UPS - 120 KVA Battery Bank - 200Ah Volt of each cell - 12 V Total No of cell - 34 No's Can you please help me to get the battery back up time for above configuration...? along with formula
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)