how to test generator protection rotor earth fault relay
and locked rotor test?
Answer / gajanan koshatwar
generator earth fault relay basically monitors the
insulation level of roror winding and shaft ground. The
rotor earth fault relay injects the low frequency pulse in
one field winding terminal wrt ground and in turn it
measures the value of refelcted pulse and claculates the
insulation value.
For testing generator earth fault relay put specific values
of precision resistors across terminals and observe the
values in relay if display is provided, or set the trip
value less than the resistace put for testing , then relay
will issue trip command and this proves relay is heathy.
Gajanan koshatwar manager Power plant
| Is This Answer Correct ? | 41 Yes | 6 No |
Why phase sequence ryb called colours.
If a 3 phase induction motor is in off condition in the conveyor and rotor of the motor keeps moving with the conveyor than the resistance of windings of motor varies. why is it so ??
why the 4 terminal are named as main, line, common, voltage (M, L, C, v) of a wattmeter?? why not its nameed as A,B,C,D??
why transformer is conneted to dc for polarity test.it doesnt work in dc?
Can we connect two or more energy meters/Amp meters on one CT set(Three phase).
5 Answers Parle, Watermark Engineering,
A double circuit with dog conductor 66KV Transmission line from wind farm evacuation to feeding substation having capacity of 25MW for transmission. Can same transmission network be considered for further expansion of Power & how much in MW. If we need to expand next 10-15 MW more will there any augmentation is required in transmission network? Kindly reply asap.
How can calculate the rating of a servo stabilizer for given a specific load
When we use air circuit breaker, it has O/L protection ,time delay SC protection, Instataneous SC protection & ground fault protection. They all have some setting range. But what is the suitable/allowable setting for the above protection which will be safe for the equipment? For example-O/L protection setting have a range of (0.4,0.45,0.5,0.55,0.6,0.65,0.7,0.8,0.9,1.0)xIn Time delay SC protection have a range of (1.25,1.5,2,3,4,6,8,10,12)xIn Time delay setting is 0.02,0.1,0.2,0.3,0.4 Instataneous setting is fixed to 20xIn Gound fault setting is given 100A,300A,600A,900A,1200A This setting are for 2500A ACB. So what will be the basic allowable setting for the above protection? is there any formulae to calculate this<
How to Calculate 11 KV Side Cable size of a 250 KVA Oil cooled transformer
how i caculate the cable size for power factor correction unit for example 300kvar
For Electrical / and Electronic Systems, when we say efficiency is 80%, then what happens to other 20% from the Power consumption.? I.e. what happens to this?
What is a DC series motor?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)