Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


how to test generator protection rotor earth fault relay
and locked rotor test?



how to test generator protection rotor earth fault relay and locked rotor test?..

Answer / gajanan koshatwar

generator earth fault relay basically monitors the
insulation level of roror winding and shaft ground. The
rotor earth fault relay injects the low frequency pulse in
one field winding terminal wrt ground and in turn it
measures the value of refelcted pulse and claculates the
insulation value.

For testing generator earth fault relay put specific values
of precision resistors across terminals and observe the
values in relay if display is provided, or set the trip
value less than the resistace put for testing , then relay
will issue trip command and this proves relay is heathy.

Gajanan koshatwar manager Power plant

Is This Answer Correct ?    41 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

what is brushless generator?

2 Answers   Jk Tyres,


I'm generating a pulse of 3V with frequency 80Hz (12.5ms time period) and pulse duration 0.125ms and feeding it to a transformer since i want the pulse to get amplified around 60V. At the output amplification s happening but the pulse is changed to a spike, can you tell me what could be the reason? (an ordinary transformer 220V-12V stepdown transformer is reverse connected ie. now it is 12V-220V stepup and voltage amplification happens)

0 Answers  


what is meant by Hrc fuses.?In the distribution system different rating hrc fuses are used for tranformer(which is 3k,6k,10k,15k etc).what is k?.plz any brother tell me about k?

1 Answers  


hi frds, i m electrical engineer.can i get cdr for electrical engineer if u have then send me on my mail id its jayesh_ee88@yahoo.com.please help me frds

0 Answers  


I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.

4 Answers  


why the voltage and current in a long transmission line are called travelling wave?

0 Answers   UIU,


Which capacitor is used in ceiling fans ?

1 Answers  


why we use the 100% and 95% stator earth fault protection for the synchronus generator ?

0 Answers   Operational Energy Group,


We have a 1275KVA existing Transformer in a power plant project. Customer want to get it test & confirm whether it is a Dyn1 Transformer or not. Pleae let me know how to test it.

1 Answers   Allied Group,


how induction generator generated the power without excition like syncronous generator.

3 Answers  


Any one can explain if there is any harm from humming noise heard from air circuit breaker : we have 415 switch board having two incomers from transformers 3.3KV/415V , when bus coupler closed, and open one ACB incomer to work in one of the transformers, the current started hunting around 50 Amps, and heard humming noise from the air circuit breaker, although the load current was only 1200 amps while the ACB capacity is 2500 Amps, and the transformer 1600 KVA. The same didn't happen when taken the other transformer offline. Why this humming noise and current fluctuation? is there any implication or danger, bearing in mind that we just returned everything back to normal and stopped the maintenance of the transformer. Shall we go ahead and ignore this noise?

6 Answers  


If we have 630kva step down transformer to operation 3 phase motor 150 kva which size of cable is used? at circuit breaker to 3 phase motor or to electrical board

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)