my question is that....few days ago i had installed a three
phase motor starter for an electric saw.the motor will run
and make the hydraulic pressure which will be goes to
pressure cylender by up and down lever.two number of
limitswitches are also installed on cylinder for safety of
motor.now when the arm of cylinder reaches to the upper or
lower limit it will cut the motor's line.and motor will be
stop.now wana know that what will i do that motor runs
continue after the limitswitch cut it down but it shold not
be made any pressure.pls answer me in brief.
Answers were Sorted based on User's Feedback
The motor is driving a hydraulic pump.Install a relief valve
set at the correct pressure in your hyd system where the pump
can perform its task but when the piston reaches the top the
pressure build up will be too high and the excess pressure is
released through the valve, the limit switches wont be
necessary any more.the pump will be running all the time.
| Is This Answer Correct ? | 0 Yes | 0 No |
c0ntr0l its up and d0wn s0len0id valve thr0ugh limit switc..
| Is This Answer Correct ? | 0 Yes | 0 No |
There should be some way to vent the excess pressure built by the motor. So first of all you should have a pressure gauge or sensor to read the pressure. Then you should have either a re-circulation line in the system or vent valve to channel the excessive pressure. When the hydraulic pressure reaches a set limit the re-circulation valve should open and channel the excessive pressure back to the tank/reservoir. In this way you can keep the motor constantly on without causing damage to system.
| Is This Answer Correct ? | 0 Yes | 0 No |
Explain the Term in CT Name Plate – Class: 5P10
how to test YNyn0 vector group in transformer?
why d.c motor speed decress with increass in load?
The Q-facr o of a coil given as wL/R. what will be shape of Q versus frequency graph.
what is phase to phase fault? what is line to line fault?
2 Answers Phoenix Technologies,
in the directional overcurrent and earthfault protection,normally we are setting the angle 45 deg lead for phase fault overcurrent and -45 deg lead for earthfault fro forward direction.but both the fault are operating on the same angle region only.why?how the relay will response?
if current required for triggering thyristor at -30 degrees(temp) is 80 mA, what is the current required at 60 degrees
Why use prefer Dc drive in place of Ac drive for kiln Operatio in Cement Plant?
mounting of bucholz relay engle on transformer
Slip at maximum torque depends on A rotor resistance and reactance B stator reactance C load current D stator resistance
why fuse is not used in neutral...
What is percent age of scrap of wires as per IE Rule Clause No in wiring for House and Industrial wiring ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)