I have one problem for masoneilan displacer type LT.I give some imformation in data shéet given for liquid level range 0 to 600 mm and sg .955 problem is 0% is ok 25%(23%) or 50%(48%)and 75%(73%) and 100% is ok this is up value and down value all ok so please halpe me
Answers were Sorted based on User's Feedback
Answer / rijesh
i hope that your calibration liquid you using is water[sg=1]. and your service sg=0.955.if so it is give you the output as per your observation
please make your calibration sg and service sg same value.
if you using service sg =0.95 and you using water for a measurement your maximuma span will be 95% and accordingly step change will effect.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / muhammad nasarullah khan
Hi Dear.
As you mentioned here taht transmitter's out put 0% and 100% (SPAN) is ok, but inbetween outputs having errror. So you are facing withe " LINEARITY PROBLEM "means out put is not linear , and that always should be linear. so go to linearity section by HART communicator ,hopefully I have answered your question.Regards
| Is This Answer Correct ? | 2 Yes | 4 No |
difference between transducer and converter in instrumentation
What is difference between “Fault Tolerant” & “Fault avoidance” PLC? Application where these system s are used?
Please anyone answer my question, what is the difference between single acting and double acting control valve, in what condition we better choose single acting rather than double acting
what is maximum vaccume?
what is the difference between dcs & plc
explain key exchanges in all security modes WPA,WPA2,TLS?
What is the definition of direct acting valve & reverse acting valve
how can we measure the level measurement with the help of pressure gauge?
WHAT IS THE MASS FLOW FLOW METER
i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to bottom & L.P. side connected to the top , so tell me what will be THE URV & LRV of that D.P. transmitter?
what is the use of conrol cable..?
What is the working principle of sox, nox analyzer?(opacity monitor) Otherwise how to measure the sox,nox?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)