How flow control valve is working with pnuematic positioner
and I/P convreter from command is given from remote
Answer / carl_ellis
A controller (the remote device) generates an electronic
4-20mA output signal which tells the valve what its position
should be.
The 4-20mA signal is an input to an I/P
(current-to-pneumatic) transducer, which creates a pneumatic
output signal proportional to the 4-20mA electronic signal
from the controller, probably a 3-15psi pneumatic signal.
The pneumatic control signal is an input to the pneumatic
positioner, which mechanically senses the valve's position.
The positioner drives the actuator with as much supply air
pressure as is necessary to drive the valve to position
demanded by the control signal.
Carl Ellis
Measure First
| Is This Answer Correct ? | 2 Yes | 0 No |
how the arrangement of equipments done in control room
What is the difference between sdv and bdv ?
If relative y axis vibration sensor is by passed, and relative x axis and absolute sensor is left working. how much monitoring i would have risked?
What happen if we install my pressure transmitter below the elevation of pipe in natural gas service?
Where should we terminate the shield and why?
Why integral control mode call Reset controller?
How is SmartPlant Instrumentation related to INtools?
what diffrence b/w plc s7200,300,400
Give Detail information about plc,dcs,and scada system?
meaning of SMART
line up procedure for dp type flow transmitter?
T.x range -0.1 to 0.2 milibar,so how much mili ampear at 0.1 milibar?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)