Do you know how to measure the earth resistance? if so
explain it
Answers were Sorted based on User's Feedback
Answer / dinesh. r
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
| Is This Answer Correct ? | 478 Yes | 30 No |
Answer / shanmu
Earth Resistance is measured by the device'EARTH MAGGER'.
| Is This Answer Correct ? | 300 Yes | 121 No |
Earth resistance can be measured using Megger instrument.
| Is This Answer Correct ? | 335 Yes | 180 No |
Answer / r.sarkar
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm.
| Is This Answer Correct ? | 116 Yes | 19 No |
Answer / dinesh kumar
1.To measure earth resistance we use Earth Resistance
Meter/Megger.
2.In this Megger there are three terminals
Line,Nuetral&Earth.
3.Line & Nuetral are connected to two terminals and EARTH
Terminal to earth pit to be measured for resistance.
| Is This Answer Correct ? | 169 Yes | 77 No |
Answer / ullas
using two methods:
1.fall of potential method
2.earth tester(device)
factors affecting earth resistance are
1. Shape & material of the earth electrode.
2. Depth of the electrode at which they r burried in soil.
3. Specific resistance of the soil surrounding the electrode
(Specific resistance of the soil varies depending on
moisture content in the soil..... varies from 80*10^3ohm-m
to 80*10^6ohm-m)
| Is This Answer Correct ? | 74 Yes | 19 No |
Answer / k.viswanathan
Actually the Earth resistance is measured using "earth
resistance meter". In previous answers some said that using
megger, but megger is used only for high resistance
measurement i.e., in Megaohms but when considereing upon
earth resistance it should not exceed 1ohm so earth
resistance meter is required.
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 55 Yes | 12 No |
Earth resistance measured by using earth tester.
| Is This Answer Correct ? | 40 Yes | 12 No |
Answer / natarajan
In this meter there will be four terminals(E, P1, P2, P3)
in which E and P1 will be shorted and connected to the grid
or electrode and P2 and P3 are reference electrodes which
will be kept on the earth surface on two different
locations for taking the reference resistances of the earth.
The meter shows the resistance of the earth. But it is
neccessary that it should be below 1ohm
| Is This Answer Correct ? | 24 Yes | 15 No |
Why grounding is generally done in supply end?
If we need 4c× 50mm sq cable but it's not available so we can pull 4c×25mm sq two cables?
Difference between SHORT CIRCUIT and an OVERLOAD ?
Why can't we take NO LOAD TRIAL of motors having V1 mounting??
HOW MUCH KVA DG SET REQUIRED for charging 12v 4000 ah battery?
Why does the rotor rotate?
1 Answers Machino Polymers, OPTCL,
11kV capacitor bank of rating 2.4KVAR, is charged with protective relays of only over current & Earth fault &.......without Over Voltage, Under Voltage & Neutral Displacement Relay. Is it advisable??
Is a 300w induction motor used in a food processor as powerful as a 1000w DC motor.
How to calculate current carrying capacity of copper conductor _ such as cable size 25sq mm,50 sq mm, 75 sq mm, 100 sq mm
Wheather there exist any dc transformer
IN a transformer during power supply how the LV and HV bushing works??
What is the diffrece between CAPACITOR BANK & CAPACITOR OF MOTOR?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)