Do you know how to measure the earth resistance? if so
explain it
Answers were Sorted based on User's Feedback
Answer / syed ahmed
i dont know so thats why iam asking how to measure the
earth resistance.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / segun
yes this is done using resistivity meter(terrameter) with
fou electrode,
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / mahesh m
Earth resistance is measured by using earth Resistance
meter. it is using for four probe method.Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.for current.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / balaji
earth resistance is measured my earth megger instrument. it
has three terminals
1) earth
2) line
3) ground
in this ground is for meter protection and earth is meant for
point of starting of measurement , line is meant for point
until which the earth resistance to be measured
this works on principle that emf generated by the generator
is forms a close loop when the points between earth and line
conducts that is meter will indicate zero incase of the
failure of earth resistance
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / sandeep
@R.sarkar
can you tell me at what distance and angle the two reference
electrodes P2 and P3 can be placed.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ankush shedge
Earth resistance is calculeted or measure by only Earth
Resistance Meter and that meter is prepared for specialy
earth resistance checking.Earth resistance must be less
than 1 Ohm if resistance increses Earth-Nutral voltage is
increses so maintain the earth nutral voltage resistance is
required less than one Ohm.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / amit lukka
The answer written by By Mr.R. Sarkar & Mr. Dinesh R. are similar and correct, one thing is to be added that P2 and P3 are reference electrode and are placed 50 Ft. away from the pit and another reference will be 100 ft. from the pit and deep 1 meter.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / dr. joshy jose
Earth resistance is mwasured by using earth resistivity
meter. It is by using four probe method. Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.
| Is This Answer Correct ? | 19 Yes | 21 No |
Answer / rajshekhar jangnure
there are four terminals p1,c1,p2,c2 outof this earthing
electrode connected to p2 and p1 &p2 get shorted There are
three electrods which are 60 to 70 feet equal distant from
eachother along withearthing electrode whose earthresistant
tobecalculate .then set 10 oham range & connect all
electrodes as mentions above by 1.0sq mm wire & rotate the
handle with constant speed & note the
reading
| Is This Answer Correct ? | 10 Yes | 18 No |
Answer / prashant
earth resistance measure can using megger instruments
| Is This Answer Correct ? | 75 Yes | 89 No |
what is the full form of MEMO? name of memo train.
The shot circuit in any winding of transformer result? Explain
What is the role of a Production Engg in a Industry?????
If there is major % of Voltage harmonics in the system, how can it be control or reduced?
Where double earthing is required? Is there any power specification to have double earthing?
What is different between Regulator & Stabilizer?
the power loss in an overloaded line is mainly due to? a. resistance b. capacitance d. inductance d. none
how many desk top computer can connect to a 25kva 3phase generator?
Whether amorphous core transformer is available in India?.If available then up to what rating of voltage and KVA?.
0 Answers DAE, Tata Chemicals,
why do some transmission towers have two insulators at one side and three insulators at the other side
Transformer/insulating oil tester(BDV tester)
list of tests to be carried out at manufacturers end while purchasing a step up transformer of 11kv to 66kv ,2MVa Capacity.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)