Answer / syed ahmed
i dont know so thats why iam asking how to measure the
earth resistance.
| Is This Answer Correct ? | 3 Yes | 4 No |
Answer / segun
yes this is done using resistivity meter(terrameter) with
fou electrode,
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / mahesh m
Earth resistance is measured by using earth Resistance
meter. it is using for four probe method.Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.for current.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / balaji
earth resistance is measured my earth megger instrument. it
has three terminals
1) earth
2) line
3) ground
in this ground is for meter protection and earth is meant for
point of starting of measurement , line is meant for point
until which the earth resistance to be measured
this works on principle that emf generated by the generator
is forms a close loop when the points between earth and line
conducts that is meter will indicate zero incase of the
failure of earth resistance
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / sandeep
@R.sarkar
can you tell me at what distance and angle the two reference
electrodes P2 and P3 can be placed.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / ankush shedge
Earth resistance is calculeted or measure by only Earth
Resistance Meter and that meter is prepared for specialy
earth resistance checking.Earth resistance must be less
than 1 Ohm if resistance increses Earth-Nutral voltage is
increses so maintain the earth nutral voltage resistance is
required less than one Ohm.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / amit lukka
The answer written by By Mr.R. Sarkar & Mr. Dinesh R. are similar and correct, one thing is to be added that P2 and P3 are reference electrode and are placed 50 Ft. away from the pit and another reference will be 100 ft. from the pit and deep 1 meter.
| Is This Answer Correct ? | 0 Yes | 1 No |
Answer / dr. joshy jose
Earth resistance is mwasured by using earth resistivity
meter. It is by using four probe method. Two electrodes
for potentials and the other two for currents. There are
two methods, viz. Schlumberger method and Wenner method in
which two types of electrode assembly. There are special
formulae to calculate the resistance from the apparent
resistivity we get from the instrument. There are special
software to interpret the data.
| Is This Answer Correct ? | 19 Yes | 21 No |
Answer / rajshekhar jangnure
there are four terminals p1,c1,p2,c2 outof this earthing
electrode connected to p2 and p1 &p2 get shorted There are
three electrods which are 60 to 70 feet equal distant from
eachother along withearthing electrode whose earthresistant
tobecalculate .then set 10 oham range & connect all
electrodes as mentions above by 1.0sq mm wire & rotate the
handle with constant speed & note the
reading
| Is This Answer Correct ? | 10 Yes | 18 No |
Answer / prashant
earth resistance measure can using megger instruments
| Is This Answer Correct ? | 75 Yes | 89 No |
What is the range of the stator resistance of 3 phase induction motor?
what does hapen if suddently frequency doubled
how to calculate multiplying factor with ct ratio 400/5
dielectric strength of vacuum is greater than SF6 but for 132Kv uses sf6 breaker & for 33kV uses vaccum breaker why such a contradiction?
2 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Suppose i Have an Ac motor of 25Hp 1500 Rpm 50 Hz Can i run a motor 2500 Rpm by AC drives by increasing a frequency either it safe or not ....
what are the oils used in transformers cooling? n which type transformer is used in power systems?
I have 10 amp MCB for my air conditioner of 1.5 ton capacity. When I connect the ac direct it is started running but when connected through stabliser the Mcb Get trip and air conditioner couldn't start.please confirm whether Mcb is required to be upgraded to 20 amp. There is no fault in ac and the stabliser. Please advice the reason of tripping the mcb when connected through the stabliser.
Hello friends., my question is related to testing of current transformer... A Ct having knee point voltage of 750 volts., and I have two step up transformer's of rating 230 v to 440 volts., can I obtain the value of 750 volts by using the two transformer's.... If yes then how could I connect the transformer's to obtain knee point voltage?? thank you in advance
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
Diagram and details of polarity test for Current Transformer 11kv 400/200/100/1A
Why Alternator has 0.8 power factor?
For R-L or R-C ckt,time constant formula is L/R and RC respectively and its unit is in sec.Pls tell me the derivation
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)