Answer / sheikh
this is not possible that without any reason motor going to
be off . your star delta control or power circuit may be
wrong other wise motor may be faulty.
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / ashok
Control circuit wire is loose conection..
Check the control circuit wire,in adanblock and
Coil side...
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shiva
check the olr its may trip inside the panel board..
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / dinesh kumar
check the load amps of the motor and bearing conditions of the motor and the olr current settings and check the terminal loose connections
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sakthivel k
Check the load current there may be a chance due load side issues. Also check for the motor noise is there any noise in bearing / housing. You may also check the load coupled/connected with this drive.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / julhash ali ahmed
Check the relay capacity. Motor may be stakes.Relay range will be 14 to 18
| Is This Answer Correct ? | 0 Yes | 0 No |
what reactive how to maintain
IN bateery size of positive is biger than negative .why?
During Starter Panel Com missing I Found The Main Incomer 40Amp MCB 10KA Trip When Motor Change Star To Delta Motor Rating 20HP BUT When We Use Same MCB To Other Motor It Does Not trip Or What Is Necessaries for Star Delta Starter MCB SFU MPCB OR MCCB And What are The Breaking Capacity of MCCB in the Motor above 15HP
HOW MUCH CURRENT CAN CARRY A 50 kvar DELTA CAPACITOR BANK?
Define sensitivity?
How to Calculate IKW(input kilowatt)of a Chiller plant
What happen to alternator if prime mover fails?
What is the main use of rotary phase converter ?
What willbe change in programming when we use 5/3 solenoid inplace of 5/2 in operating of a cylinder?
Why we are designed only 11Kv and 6.6Kv Alternators, not 33Kv Alternators and Power Transmission side we are designed only 220kv, 120kv, 66kv, 33kv, 11kv, and 440volts, not 20kv, 50kv, 100kv.
why voltage drop will occurs in 3 phase line?
for 11KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV OH system what will be typical per KM "R" "L" "C" parameter. for 33KV UG system what will be typical per KM "R" "L" "C" parameter.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)