If the kvar rating of capacitor bank is
600 kvar at 525V then what it's rating at
415v.
Answers were Sorted based on User's Feedback
Answer / ahamadkutty
THE MAXIMUM CURRENT RATING OF THE 600kVAR CAPCITOR IS
600000/525/1.7321= 660 AMPS.SO AT 415 VOLTS LIMITING THE
CURRENT TO 660 AMPS THE RATING WOULD BE 415x660*1.7321=
474.3kVAR
Is This Answer Correct ? | 2 Yes | 0 No |
what current is taken from a double wound 500kva transformer
We have 800KW motor operating at 6600Volt,50 Hz supply.During 1st startup it tripped on overcurrent trip.It's FLA is 88 Amps.The K factor of Thermal overloaaad was set on .94 initially.then we set at 0.97 and then it started fine.i dont understand why it tripped first?What are the protections which comes in picture during starting ?
Why overhead transmission line in triangular shape?
what will happen when square wave is fed into input side of 3kva transformer and what you will get on output side.
WHY ARE THE LT GENERATORS SOLIDLY EARTHED WHILE THE HT GENERATORS ARE EARTHE THROUGH NGR OR NGT??
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
Impedance relay is directional relay or non directional relay?
what is the difference between inductive load and capacitive load?give me some examples in general
how do i calc busbar size for a rated current?
Mechanism of Wye Delta Starter?
How to calculate total harmonic distortion level(THD) in VFD? and how can we reduce harmonics?
what is ht breaker