Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why star point of motor shall not be grounded?

Answers were Sorted based on User's Feedback



why star point of motor shall not be grounded?..

Answer / ranjit kumar mallick

In induction motor the rotor movement is due to it's
interaction with the stator resultant rotating magnetic
field flux and the resultant magnetic flux is due to the
three phase closed circuit. Once we ground the star point
the resultant magnetic field will drop and it becomes
extremely dangerous in case of fault as motor will run at
low speed without triping due to the current path available
to ground.So it will draw high current

Is This Answer Correct ?    6 Yes 3 No

why star point of motor shall not be grounded?..

Answer / sarwar

Star point of motor is not necessary to ground because a
motor is a balanced load.So,no current will flow through
star point to nutral.

Is This Answer Correct ?    7 Yes 4 No

why star point of motor shall not be grounded?..

Answer / vishwanath chothe

Grounding a motor star point will create an earth path for earth leakage current to flow through that motor's star point. If there are 10 motors in a process plant and their star points are all grounded, there are 10 additional paths for earth leakage currents to flow through.
If all the motors' star points are grounded in this way the earth fault current detections by the protection relays will be complicated and likely they will trip at the incorrect locations because earth fault currents are flowing in many directions toward multiple grounded neutral points.

Therefore the electrical consumers (ie the load, including the capacitor banks), even if they are star connected, are not to be grounded.

Is This Answer Correct ?    1 Yes 0 No

why star point of motor shall not be grounded?..

Answer / nadeem

Bcoz star point make additinal loop to source volatge and leads to burst the motor...

Is This Answer Correct ?    0 Yes 0 No

why star point of motor shall not be grounded?..

Answer / suresh

if unbalance current in motor then motoe burnt due to the
y point earthed

Is This Answer Correct ?    3 Yes 5 No

why star point of motor shall not be grounded?..

Answer / raju_

STAR CONNECTED WINDING IS CLOSE LOOP CIRCUIT IT SELF IF
YOU TRY TO GROUNDED THEN CRIRCUIT NOT GOING CLOSE THEN
MOTER WINDING IS NOT GENRETED E M F AND MOTER
CANT'PERFORMING WELL! THATS WHY WE CANT GROUNDED THE STAR
CONNECTED WINDING.

Is This Answer Correct ?    1 Yes 5 No

why star point of motor shall not be grounded?..

Answer / rsjendran

The star point of the motor can not be earthed since fault
currents from other systems may enter in to the motor
circuit ....

but normally motors are not protected againest this...

since it is advisable to ground the star point of the motor

thanks

Is This Answer Correct ?    1 Yes 6 No

why star point of motor shall not be grounded?..

Answer / sai

In the internal winding of the terminals shorted as a
nutral is Act to as earth.

Is This Answer Correct ?    2 Yes 9 No

Post New Answer

More Electrical Engineering Interview Questions

how to calculate short circuit breaking capacity KA for 2500kva 33kv transformer.

0 Answers  


If short circuit ratio is high is it bad or good for a machine then tell the reason...

0 Answers   Bhel,


what the effect will occur if we increase the airgap in induction motor

3 Answers   ONGC,


I have a CT meter with ratio 60/5. The meter reading of previous month was 3290.49 and that of current month was 3797.26. How many chargeable units as per normal meter should be my reading.

0 Answers  


can any one help me for my ups inter view , list out few basic technical ups question with answer.

1 Answers  


What happen when switch yard one pole not tripe when you tripping the breaker

3 Answers   Adani,


why ohmas low not sutable to transformer.

1 Answers  


What is IDMT relay how it works.

3 Answers   Electrotherm, Sulzer,


what is voltage ?

7 Answers  


What is the minimum load that you can keep in a 3 Phase 40 KVA Diesel Generator? Is it neccessary to load all the 3 phases? Can a phase be left without load?

2 Answers   DRDO,


what is the similarity and difference between ups and inverter?

4 Answers   GMR,


what is corona

3 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)