Answer / laxmikant
Question is not clear,
Because 200kVA/(1.732x0.415kv)= 278.24 Amps/phase.
Please check. If you load demmand is 200kVA , as DG runs
always with 89% efficiency @ 100% load, You may choose for
250kVA DG.
| Is This Answer Correct ? | 2 Yes | 0 No |
What is skin effect?
Sparking occur when a load is switched off because the circuit has high – a.) Inductance b.) Capacitance c.) Resistance d.) None
4.In which type of welding is a pool of molten metal used.....
3 Answers ISRO, SSC, Vizag Steel,
how can we find of cable capicity in amper?how much ampere withstand by 300sqmm cable?
how work the lighting arrestor?
our industries ht line so power fluctation(once drop of power please rectify causes
what is the defination of electrical engineer.
I have a 25 KVar capacitor bank at my facility.How to check the capacitor bank ??
Hi all I had applied for the RRB test in the ELECRICAL category. I would be pleased if any of you can sent me previous year question papers. Please forward the question papers to varshashahi@yahoo.com Thanks and regards Varsha
What is meant by system?
What is meant by TAN-DELTA test carried out in motors?
HAI,I HAVE 6,60KW MOTOR FEEDERS IN MY MCC PANEL.HOW CAN I DO MY SETTINGS FOR OVERLOAD,SHORTCIRCUIT,GROUNGFAULT,INSTANTANEOUS TRIP FUNCTION IN MY 4000A CIRCUIT BREAKER?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)