how to set calibration range in a DP transmitter to measure
level for a closed tank and for an open tank,and also please
explain me how to set calibration range for a DP flow
transmitter in a line ?
Answer / carl_ellis
Configuring the range for a DP transmitter
Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.
Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element
Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.
| Is This Answer Correct ? | 2 Yes | 5 No |
EXPLAIN PROPOTIONAL INTEGRAL DERIVATIVE CONTROL ACTION?
I have a MRE200 amplifier for controlling a mitsubishi servo motor, I would like to know how many pulses are required to rotate the servo motor by 1 degree and what must be the pulse width
what are the three main programming languages in plc
Hi my friends Is any one who can assist me in knowing the typical interview questions for system engineer at General Electric pty Ltd
give classification of transducer based on type of application
how can we understand about dcs "bailey infi 90 dcs system" . how its work how signal come from field how it process and how o/p creative by controller. how its cards work.the bsic principle of working of dcs
Can anybody tell me the exact explanation for Functional calibration?When it should be done on process or on lab? Advanced Thanks
how can calibrate vacume trasmitter by HART COMMUNICATOR ?
I faced several time siemens ps2 positioner automatically getting Chang in it's set point direction after auto calibration So is there any causes biside this or any permissives ?
Any one can help me to identified, how can we interchange the device in FF
what is the deference bitween DCS and PLC SCADA HMI System for Power Process Industry.
WE ARE HAVING YOKOGAWA CENTUM CS 3000 DCS, 2 FCS AND 4 HIS " When the operation Download to HIS message appears: Equalize start. HIS0163 WARNING: Could not connect to equalize destination. (7001) Retrying. Number of retries = 0/1 ERROR: LdXopsLoadMain: connect error 10060 ERROR: LdXopsLoadMain: connect error 10060 ERROR: Processing terminated due to connection error. (7002) Equalization end with errors. HIS0163 ---- ERROR = 3 WARNING = 1 ---- Tell me, please, why and how to solve the problem."
6 Answers Khas Pvt Ltd, Yokogawa,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)