how to set calibration range in a DP transmitter to measure
level for a closed tank and for an open tank,and also please
explain me how to set calibration range for a DP flow
transmitter in a line ?
Answer / carl_ellis
Configuring the range for a DP transmitter
Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.
Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element
Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.
| Is This Answer Correct ? | 2 Yes | 5 No |
If the Barrier Fails during online then What will be the control valve position in field or Positioner action in the field.
principle of rtd
Hi my friends Is any one who can assist me in knowing the typical interview questions for system engineer at General Electric pty Ltd
any body who gone thru recent iocl interview.INSTRUMENTATION questions. I need.
How to convert mA into Percentage?
1. Pl. send details about different types Gas Analyser, like Co2, O2, SOX/NOX, etc. with calibration procedure. 2. How to calibrate H2S gas detector in field?
any one can send me instrumentation previous interview papers? I prepare for MNC Company Interviews? my mail id- Rakesh.Golla@dodsaldxb.ae , and another mail rakesh.gvk@gmail.com
what is control valve input and out put
WHAT IS DOPPLER EFFECT? WHERE IT IS APPLIED?
what is the control valve?how many types of control valves are there
6 Answers Chemin, Hindustan Zinc,
In Increasing temperature why thermocouple used and RTD is not used. Both RTD and Thermocouple have in Range of uses.
Why flow/pressure transmitter before control valve?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)