how to set calibration range in a DP transmitter to measure
level for a closed tank and for an open tank,and also please
explain me how to set calibration range for a DP flow
transmitter in a line ?
Answer / carl_ellis
Configuring the range for a DP transmitter
Open tank:
- Flanged DP transmitter
- high side at lower flange
- no remote seals:
- units: water column units = uwc
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
Closed tank:
- flanged DP transmitter
- high side at lower flange
- no remote seals
- dry leg from vapor space above liquid is piped/connected
to the low side
- LRV = 0.00 uwc
- URV = physical upper level elevation (uwc) * specific
gravity of fluid
When the receiver (DCS/PLC/indicator/recorder) receives the
level signal, it converts to physical level elevation by
dividing the process level signal by the specific gravity
and scaling to physical level units.
Volumetric flow rate with DP transmitter on DP flow element:
- units: water column units = uwc
- LRV = 0.00
- URV = maximum DP value at the maximum flow rate stated
on the sizing sheet of the DP flow element
Whether the signal is square rooted in the transmitter or
in the receiver for conversion to flow rate is up to the
plant convention/standards.
Is This Answer Correct ? | 2 Yes | 5 No |
Draw block diagram BOILER COMBUSTION loop & Explain
1 Answers Bajaj Hindusthan, Exxaro,
how can I install "operating system " in may HART communicator? It is damaged, and it doesn't boot up.
installation process of orifice,a question asked for confusion creation in interview by BARC 1.if orifice is tightly fitted with pipe ,it will act like venturi 2.if orifice is left hanging in between liquid it will not create the pressure difference exactly,
If an Instrument has 550 ohm internal resistance and the cable used for that instrument is 0.5 ohm per meter resistance. If the voltage is 12volt.How much length cable can be used? Please tell me its Calculation formula.
admittance level sensor meaning?
Please why do we use 4-20ma in instrumentation engineering
if in a level tx height is given, how u calculate the ranges of the tx?
2 Answers Bombay Rayon Fashions, Invensys,
please can any one tell me clearly about pid tuning i am confusing about this .how to tune pid easly?
which are types of orifice tap ?
what is meant by calibration
Yokogawa dcs nodes advantages?
in sulfur process what is material of impulse line we use to connect with transmitter ? and does teflon affected by sulfur?