hello dear ,
well u can use -10 volt ,bt main reasion is tha because of we using the i/p supply is -24 and its reasion is that we are using in that pnp and pnp bias is always negative ,we can use
positive npn ,bt the bently had modulded in negative ,so we are set to on -10 volt.
Is This Answer Correct ? | 22 Yes | 5 No |
Answer / r.murugan
Vibration sensor output based on your probe gap
normal refrence from shaft and probe gap +1.2mm
corrosponding +1.2mm gap you will get output of the
proximitor -10v
if gap is increase voltage will increase gap is decrease
voltage will decrease
bently vibration probe calibration there is kit TK3-2E
PROXIMITOR POWER SUPPLY VOLTAGE -24V DC (THIS ONE PNP
FUNCTION BASE)
Is This Answer Correct ? | 15 Yes | 2 No |
Answer / velu
Gap will increase voltage will increase in negative
Is This Answer Correct ? | 2 Yes | 2 No |
how to calibrate and troubleshooting of leveltroll?
How Honeywell FSC is functioning and what is its purpose? Can we bypasa it and only use DCS instead of that.
Can I put my meter across an RTD to check it safely witout tripping the equipment when it is connected to an monitoring device eg.RTD module or IQ 1000
what are the on/off valve precaution?
Why hunting will occour in control valve?
What is negative range in transmeter?
i want to measure temp of hot sand(welding flux) in closed chamber(around 150 deg C).Which is better thermocouple or thermometer?
A pressure transmitter with a range of 0-100 bar.The accuracy of the instrument is 1% of upper range value? The pressure indicating transmitter is showing the system pressure is 50 bar. b. When you include the error, what is the minimum possible pressure in our fuel gas system? i. 49.5 bar ii. 49 bar iii. 1 bar iv. 0.5 bar We want to change the filter cartridge. We must depressure the fuel gas system. c. After we depressure the system in preparation for maintenance, the transmitter displays a pressure of +0.1 bar. At this time, what is the possible range of pressures in our fuel system? i. +0.099 to +0.101 bar ii. 0 to +0.2 bar iii. -0.1 to +0.3 bar iv. -0.9 to +1.1 bar
how can we measure the pressure in underground cooling water pipeline by using pressure transmitter?what about the tapping position?
which types of oxygen analyzer describe with drawing ?
why 4-20 mA in covection system?
why we use only 4 to 20ma other than 0 to 16 ma