Answer / alf
Poorly worded question.
1) The VSD (Inverter) is connected to an external supply at 400V, 3ph, 50Hz..
2) UDC+, UDC- (R+; R-) are the terminals for connecting an external brake. The voltage on these terminals is over 500Vdc and is supplied FROM the VSD, not connetected TO the VSD
| Is This Answer Correct ? | 0 Yes | 0 No |
How can we calibrate the level interface for Fisher® FIELDVUE® DLC3000?if use water to calibrate and our liquid SG are 0.75 and 1 ,Displacer height=14" and How much should be set SG in trasmitter during calibrate,for URV and LRV how shold be set
POSSITIVE PULSE IS APPLIED TO AN INVERTER INPUT.THE TIME FROM THE LEADING EDGE OF THE INPUT TO THE LEADING EDGE OF THE OUTPUT IS 10 ns. THE TIME FROM THE TRAILING EDGE OF THE INPUT TO THE TRYLING EDGE OF THE OUTPUT IS 8 ns. WHAT ARE THE VALUES OF tPLH and tPHL?
i have one temperature TX in my loop check time once i was remove elament temp gose maximum then i am conect corectly but still now temp showing maximum what can i do this problem?
hi everybody. right now i am working with thermal power plant. our company plant is tripped because of program corrupt. i would like to know is it possible when the plant is running. we are using FREELANCE ABB800F CONTROLLER.
How a oxygen sensor & analyzer work at boiler or furnace, whats the principle & science is beyond this,How O2 sensor sence & convert signal & move toward analyzer & analyzer show reading in percent?
rtd principle?thermocouple principle?
how can be calibrate flow indication transmitter (rosemount) it shows excess milli amps nearly about 24 ma on full scale, but its scale was set on 20ma on full scale..???how can be simiulate..???
EXPLAIN PROPOTIONAL INTEGRAL DERIVATIVE CONTROL ACTION?
Name different parts of a pressure gauge. Explain the use of hair spring in the pressure gauge.
While preparing the graphic diagrams trend display, 3 types of trends are prepared by Yokogawa system vender. These are for process variable, manipulated variable & set point variable. Why these 3 trends are required? Explain the purpose of these 3 trends.
what is the difference between two wire transmitter and 4- wire transmitter
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)