In split range control, we will control 2 outputs with time
interval. Eg :(with 4-20 ma signal, for 4-12 ma we are
operating one control instrument like valve & for 12-20ma we
are operating other control instrumet (other valve). If we
get a signal of 15ma to first instrument (Valve 1), what
will happened to the first valve, and if we get signal above
20 ma to 2 valve what will happened ?
Answers were Sorted based on User's Feedback
Answer / kyle condran
It depends on the setup the 2 above post both correct the following scenario can also be seen sometimes.
Valve 1 set for 4-12mA (100% open @ 4mA and 0% open at 12mA)
Valve 2 set for 12-20mA(100% open @ 20mA and 0% open at 12mA)
For example if you have a temperature control with 2 valves one controlling steam and one controlling chilled water, going into a heat exchange process, when we want to increase temp out of heat exhanger contol signal goes up towards 20mA chilled water valve closes and steam valve opens. when we want to cool the process down the opposite happens and the control signal falls towards 4mA the steam closes and chilled water valve opens.
so 4mA is full on chilled water 20mA is full on steam 12mA is both closed.
lets assume fail open cooling / fail closed heating valve.
as for 15mA on valve 1 depending on where the split range is done, ie controller or valve.
for our example if done in valve it will ignore anything above 12mA and be fully closed.
above 20mA in our example will be ignored by valve 2 since it is allready at 100% at 20mA.
see http://www.contek-systems.co.uk/Documents/split_range_control.htm for the first 2 post
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / romeo
The first valve will open fully open (100%) and the second
valve will open at about 37.5% only.
| Is This Answer Correct ? | 1 Yes | 2 No |
Answer / pramod suwalka
1. at 15 ma signal first Valve open fully.
2. at 20 ma signal Both Valve open fully.
| Is This Answer Correct ? | 1 Yes | 5 No |
Explain what is meant by the term “FLASH POINT” of liquid?
A length of steel pipe is used to carry sea water to a desalination plant. An adequate corrosion allowance must be specified and indicated in the piping specification, which affects the _________________________ of the pipe
send me model hpcl questions pleas..........my mail id mohideen.dharvesh@gmail.com
What is defferent betwen ESP &PCP PUMP .HOW IT IS WORK?
My flow transmitter range is 0-1000mmwc.DCS range is 0- 100m3/hr.What is correspond out put in terms of milliamps if my flow is 65m3/hr
what is 24vdc live and dry supply
What are the maximum packet size of: a) HART b) Profibus DP c)Profibus PA d) DeviceNet e) Foundation Fieldbus
What is the reason PT speed not incresed in gas turbine?
can u briefly explain aboutan aryton shunt multirange DC ammeter?
how to change 4 wire rtd transmitter into a 3 wire rtd transmitter? as our transmitter is working for 4 wire rtd, what should do for working on 3 wire rtd transmitter
we are used SAMSON 3730 Smart positioner.please tell me how to calibration this.
describe yourself?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)