Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can
u give me Answer.

Answers were Sorted based on User's Feedback



How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / naren

connect to pressure calibator, apply the low pressure -60
adjust the span into low pressure and then apply the high
pressure then adjust the span screw into high value. it is
calibrated in the range of -60 to -20.

if it is the SMART transmitter its easy, just apply URV and
LRV value through Communicator then connect to the pressure
calibator then check URV, LRV and intermediate value

Is This Answer Correct ?    20 Yes 6 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / ramesh

we can apply the +ve pressure to the lp side that is 60
with zero, then +ve 20 with span with respect hp open to
atmosphere

or apply -ve pressure that is vaccum to the hp side with
respect lp open to atmosphere

Is This Answer Correct ?    10 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / welcome4ujd

make the calibration set up , to get -60 , give 60 in lp
sidethen adjust zero screw, give 20 in lp side toget -20
url , and adjust span screw.

Is This Answer Correct ?    18 Yes 12 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / sn

apply -60 to the transmitter n make the o/p as 3 psi, then
giv -20 as the input n adjust the o/p as 15 psi.

Is This Answer Correct ?    3 Yes 3 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / sandeep patel

connect transmitter in bench setup, left LP side of transmitter open to atmosphere and apply -60 mmwc to HP side and check it s o/p is 4 mA or not and if it is not, then do zero trimming. then apply -20 mmwc to HP side and check o/p is 20 mA or not otherwise fo span trimming.

Is This Answer Correct ?    0 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / suresh agravat 83204 78125

Urv-LRV÷4=Span
-60=4ma
-50=8ma
-40=12ma
-30=16ma
-20=20ma
Apply pressure accroding to above chart and monitor output

Is This Answer Correct ?    0 Yes 0 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / anup ramteke

It depends upon the type of transmitter u are having. If its
HART based transmitter then either u can calibrate it
through HART calibrator. firstly go to basic set-up mode and
feed the URV as well as LRV values. And if u want to
calibrate it at field itself when HART calibrator is not
available then u can set LRV value by entering its value in
mode 2 whereas for URV its mode 3.

Is This Answer Correct ?    2 Yes 4 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / suvendu sekhar giri

You can give positive pressure on low pr side keeping the
high side open to atomosphere for lrv (-60) & urv (-20)or
you can give negative pressure on high pr side for lrv(-60)
& urv(-20) keeping low side open to atomosphere.You can
adjust zero at lrv & span at urv. If it is smart
transmitter then you can zero trimming keeping both the low
& high pressure side open to atmosphere.

Is This Answer Correct ?    2 Yes 5 No

How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can u give me Answer...

Answer / venkat

actually we can calibrate LP side by positive pressure and
Hp side also we can calibrate by negative pressure but LP
side better

Is This Answer Correct ?    3 Yes 7 No

Post New Answer

More Instrumentation Interview Questions

why we are using analytical instrument in plant ?

1 Answers  


What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?

11 Answers   Samsung,


Is there any relation between Artificial Intelligence and Instrumentation?

0 Answers  


what's the criteria of using over range protector when installing Pressure Gauge

1 Answers  


Can anyone explain in a simple way the difference between DCS and PLC?

7 Answers   Honeywell,


IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN

1 Answers   IFFCO,


what is the difference between Feedback controller and Feed forward controller. and when it is to be used.

3 Answers  


when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?

1 Answers   UETCL Uganda Electricity Transmission Company Limited,


What is the syllabus for Instrumentation Engineers, who wish to join the Public Sector Units??

1 Answers  


Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?

4 Answers   Ecil,


What is DeltaV?

2 Answers  


What is difference between profibus and modbus communication

2 Answers   GMR,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)