How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can
u give me Answer.
Answers were Sorted based on User's Feedback
Answer / naren
connect to pressure calibator, apply the low pressure -60
adjust the span into low pressure and then apply the high
pressure then adjust the span screw into high value. it is
calibrated in the range of -60 to -20.
if it is the SMART transmitter its easy, just apply URV and
LRV value through Communicator then connect to the pressure
calibator then check URV, LRV and intermediate value
| Is This Answer Correct ? | 20 Yes | 6 No |
Answer / ramesh
we can apply the +ve pressure to the lp side that is 60
with zero, then +ve 20 with span with respect hp open to
atmosphere
or apply -ve pressure that is vaccum to the hp side with
respect lp open to atmosphere
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / welcome4ujd
make the calibration set up , to get -60 , give 60 in lp
sidethen adjust zero screw, give 20 in lp side toget -20
url , and adjust span screw.
| Is This Answer Correct ? | 18 Yes | 12 No |
Answer / sn
apply -60 to the transmitter n make the o/p as 3 psi, then
giv -20 as the input n adjust the o/p as 15 psi.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sandeep patel
connect transmitter in bench setup, left LP side of transmitter open to atmosphere and apply -60 mmwc to HP side and check it s o/p is 4 mA or not and if it is not, then do zero trimming. then apply -20 mmwc to HP side and check o/p is 20 mA or not otherwise fo span trimming.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh agravat 83204 78125
Urv-LRV÷4=Span
-60=4ma
-50=8ma
-40=12ma
-30=16ma
-20=20ma
Apply pressure accroding to above chart and monitor output
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anup ramteke
It depends upon the type of transmitter u are having. If its
HART based transmitter then either u can calibrate it
through HART calibrator. firstly go to basic set-up mode and
feed the URV as well as LRV values. And if u want to
calibrate it at field itself when HART calibrator is not
available then u can set LRV value by entering its value in
mode 2 whereas for URV its mode 3.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / suvendu sekhar giri
You can give positive pressure on low pr side keeping the
high side open to atomosphere for lrv (-60) & urv (-20)or
you can give negative pressure on high pr side for lrv(-60)
& urv(-20) keeping low side open to atomosphere.You can
adjust zero at lrv & span at urv. If it is smart
transmitter then you can zero trimming keeping both the low
& high pressure side open to atmosphere.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / venkat
actually we can calibrate LP side by positive pressure and
Hp side also we can calibrate by negative pressure but LP
side better
| Is This Answer Correct ? | 3 Yes | 7 No |
Dear sir I am MD.zafar eqbal. I have taken this id from allinterwiev .com I have qustion if you dont mind. 1.what is the maximum operating temprature in instrumentation. 2. I want know about viberation i mean wahat types of sensor used in viberation And what types of trabsmitter used.and hiw to control it and wher is used of viberation transmitter and finally how to control it and what types of fault come. Sorry for disturbing you. I know you have no reason for help me. Because you dont know about me.but i request you please help me these question are very usefull for my feauture.plz sir Thanking you. Sent from Yahoo! Mail on Android
what is buoyancy law?
can someone tell me about electronic speed switch &how it conect with proximittyswitch?(with dgm)
give some question relative instrument fitter?
An atmospheric storage tank has a diameter of 20 m and a height of 8m.It is half-full of liquid with the remainder of the space containing air normally at atmospheric pressure. If the connection to atmosphere is accidentally closed off and 10 cubic m of liquid removed, what happens to the internal pressure of the tank? What are the possible consequences for the tank?
If Solenoidal valve works in manual mode but not in Auto mode. What should be the problem?
8 Answers Bharathi Cement, Titanium,
explain key exchanges in all security modes WPA,WPA2,TLS?
I want to know the questions asked in ONGC interview(after being selected in the written exam) for Instrumentation branch.Kindly help.
while am calibrating Drager polytron 2IR flame gas detector occured non zero status.how can i get zero status?
What are the logic behind 2x2 and 2x3 logic and more when ask in interviews
Is wet leg type system nessesary to measure water level of steam DRUM? How the transmitter is calibrated to measure this level?
plz exlain the dcs system of ABB sympony hamnony
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)