How to Calibrate Penumatic Transmitter.LRV= -60 URV= -20.Can
u give me Answer.
Answers were Sorted based on User's Feedback
Answer / naren
connect to pressure calibator, apply the low pressure -60
adjust the span into low pressure and then apply the high
pressure then adjust the span screw into high value. it is
calibrated in the range of -60 to -20.
if it is the SMART transmitter its easy, just apply URV and
LRV value through Communicator then connect to the pressure
calibator then check URV, LRV and intermediate value
| Is This Answer Correct ? | 20 Yes | 6 No |
Answer / ramesh
we can apply the +ve pressure to the lp side that is 60
with zero, then +ve 20 with span with respect hp open to
atmosphere
or apply -ve pressure that is vaccum to the hp side with
respect lp open to atmosphere
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / welcome4ujd
make the calibration set up , to get -60 , give 60 in lp
sidethen adjust zero screw, give 20 in lp side toget -20
url , and adjust span screw.
| Is This Answer Correct ? | 18 Yes | 12 No |
Answer / sn
apply -60 to the transmitter n make the o/p as 3 psi, then
giv -20 as the input n adjust the o/p as 15 psi.
| Is This Answer Correct ? | 3 Yes | 3 No |
Answer / sandeep patel
connect transmitter in bench setup, left LP side of transmitter open to atmosphere and apply -60 mmwc to HP side and check it s o/p is 4 mA or not and if it is not, then do zero trimming. then apply -20 mmwc to HP side and check o/p is 20 mA or not otherwise fo span trimming.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / suresh agravat 83204 78125
Urv-LRV÷4=Span
-60=4ma
-50=8ma
-40=12ma
-30=16ma
-20=20ma
Apply pressure accroding to above chart and monitor output
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / anup ramteke
It depends upon the type of transmitter u are having. If its
HART based transmitter then either u can calibrate it
through HART calibrator. firstly go to basic set-up mode and
feed the URV as well as LRV values. And if u want to
calibrate it at field itself when HART calibrator is not
available then u can set LRV value by entering its value in
mode 2 whereas for URV its mode 3.
| Is This Answer Correct ? | 2 Yes | 4 No |
Answer / suvendu sekhar giri
You can give positive pressure on low pr side keeping the
high side open to atomosphere for lrv (-60) & urv (-20)or
you can give negative pressure on high pr side for lrv(-60)
& urv(-20) keeping low side open to atomosphere.You can
adjust zero at lrv & span at urv. If it is smart
transmitter then you can zero trimming keeping both the low
& high pressure side open to atmosphere.
| Is This Answer Correct ? | 2 Yes | 5 No |
Answer / venkat
actually we can calibrate LP side by positive pressure and
Hp side also we can calibrate by negative pressure but LP
side better
| Is This Answer Correct ? | 3 Yes | 7 No |
why we are using analytical instrument in plant ?
What is the standard height for stancion supports? and what is the standard mounting height for different transmitters?
Is there any relation between Artificial Intelligence and Instrumentation?
what's the criteria of using over range protector when installing Pressure Gauge
Can anyone explain in a simple way the difference between DCS and PLC?
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
what is the difference between Feedback controller and Feed forward controller. and when it is to be used.
when the force applied on load cell the ohms will be varriying .and how its convert ohms to mv generate and have any formulae?
1 Answers UETCL Uganda Electricity Transmission Company Limited,
What is the syllabus for Instrumentation Engineers, who wish to join the Public Sector Units??
Q- voltage source of 12v is driving the circuit.if circut draw the current of 0.5A them source voltage will became 11.8v.what is the power dilevered by source when circuit draw 5A current ?
What is DeltaV?
What is difference between profibus and modbus communication
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)