What will the new flow factor if D/P Transmitter is
RE-RANGED from 25" WC to 50" WC
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
| Is This Answer Correct ? | 0 Yes | 2 No |
Pls can anybody tell me how much memory plc's has?in byte or in Kb
A DP transmitter is used to measure the level of an open tank. The drain line of the tank is connected to a control valve, and is configured as, if the level of the tank is 90% the valve should get open 10%. And if the tank level is 10%, the valve should get open 90%. Draw wiring diagram and explain how to configure DP transmitter and control valve using HART communicator. If the span error at output is 1%, what will be the %opening of the control valve at 60% level of the tank?
what is diff between sensors and transducers.explain with ex?
how can be connected thermocouple in series?what is the need?
What are the most frequent problem faces with Vortex flow meter?
how to calibrate any tansmiter by loop or hart calibrator
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
If P will increase then what will happen with PID?
1 Answers Chettinad, Galfar, Mehran Sugar Mills,
what is linerity and non-linearity?
why we use double acting valve and where?
What is the minimum rating availalbe for weld neck orifice in market?
what's the reson that,Load is not same on VFD I/P and O/P Side.whenever DOL condition load is same I/P and O/P side.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)