What will the new flow factor if D/P Transmitter is
RE-RANGED from 25" WC to 50" WC
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
Is This Answer Correct ? | 0 Yes | 2 No |
if the t/c o/p is 4-20mv then how plc recognize it because we are dealing with the 4-20ma in the plc ????????????????
What is the purpose of RS Networks
what is the analog input , analog output , digital output, digital input geven to the MSSV , CBD, IBD , START UP VENT , BOILER FEED PUMP , AOP, CEP , ETC
1 Answers Bharat Biotech, TATA,
What is seeback effect?
Hi, am aniket, I got engineering degree in instrumentation and control, but as their were no job availabilities for engineer's post I started working as instrumentation technician I kuwait, so my question is is this technician's experience worth for getting the position of engineer?
1 Answers Almeer Technical Services,
what are different types of cables used in instrumention how to calibrate a level transmitter online ( rosemount )
why we are not using the turbine flow meter in the steam service?
plz tell me clearly about PID.."when v have to change I value,D value,GAIN??
a pressure transmitter with a range of 0 to 2500kpag has a specified accuracy of 0.5 % of span.It is to be calibrated using a comparison gauge to have an accuracy of 0.1% of span.The comparison gauge has a range of 0 to 3000kpag What is the accuracy ratio? is this ratio acceptable?
What is inside the PLC panel? How does instruments communicate to DCS computer via PLC? What is the type of wiring in PLC connections? Please answer... Thanks
What is DDC-MIS?
which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?