What will the new flow factor if D/P Transmitter is
RE-RANGED from 25" WC to 50" WC
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
| Is This Answer Correct ? | 0 Yes | 2 No |
where proximity sensor installed on tank in loading arm application
generally transmitter power supply having some range(12v to 35v) but the out put(4-20 mA) must same for given input.If we vary the power supply voltage then output mA also to be change according to V=IR. Is there any voltage regulator in the transmitter ?
i have height of stem drum level 1000mm.how i calculate the DP transmitter
What is zener diode? What is voltage regulator?
please suggest me, how can i change the display setting in term of unit in place of % of Honeywell pressure transmitter ST3000S100?
why the SCAN time of DCS is more & that of PLC is less? if the SCAN time of DCS then why we use DCS.
how u calibrate pneumatic n motorized c/v?
how pressure reduce through pressure control valve? suppose we have to reduce 20 kg pressure to 10 kg pressure , then what we do ? open the valve or close the valve , initially it is 20 % is upon ( for ur knowledge ).
what is the exact job for automation enggineer?
Capacitance, resistance ( colour coding ), parallel & series circuits.
what do you mean by Loop checking ? What are the cold loop check and hot loop check? what are the difference between these two loops?
Why do we floating DC in DC system.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)