What will the new flow factor if D/P Transmitter is
RE-RANGED from 25" WC to 50" WC
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
Is This Answer Correct ? | 0 Yes | 2 No |
what is installation and commissioning of (fat & sat) of power plant dcs ? this question keeps in desirable conditions of one company .
I want to measure flow by using DP Tx and range is 0 to 1200 Kg/cm2 ?
Whatis the reset ofset and control system in instrumentation
0 Answers Asyad International Company, CAE, Sugar Factory,
can we use a control valve without positioner
what is the calibration standard for pressure and differential pressure transmitters?
What is the difference between a double acting and single acting positioner? what type of valves use single acting positioners?
1 Answers AquaTech, NamPower, Samson Resources,
What is two wire system and how it work
what is difference between E/P positioner and I/P positioner. Why E/P fixed in below actuator and why I/P fixed in other place
I am a electronics and instrumentation fresher trying for a job in IT sector. what do need to prepare for the interview?
How to zero trim the level transmitter by using foundation fieldbus communicator.
why we use the ac supply load cell>?can we use the dc supply load cell?advantages and disadvantage of the ac supply load cell?
What is the compensation of thermocouple