Answer / carl_ellis
Answer:
The flow rate at 50.0"wc will be 141.4% of the flow rate at
25.5"wc.
Reason:
The design maximum flow rate at 25.0" is 100.0% flow rate.
Flow rate is the square root of the percentage of flow at a
given DP.
The flow rate at 25.0"w.c. DP is the square root of 1.00 (or
100%)
If the DP doubles from 25.0 to 50.0, then the DP increases
from 100% at 25.0"wc to 200% at 50.0"wc
The flow rate at 200% DP increases by 141.4% because the
square root of 2.00 (or 200%) is 1.414.
Carl Ellis
Measure First
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / enka group iraq
Ans;- A simple calculation is as follow :- Q1 / Q2 = √DP1/√dp2
Q1= Q2 X √DP1/√dp2
Q1 = new flow factor, Q2 = existing flow factor
DP1 = transmitter new range DP2 = transmitter existing range
Q1 = Q2 X √50/25 = Q2 X 1.41
The new flow factor will be 1.41 times higher then the existing flow factory
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / selva
The ratio of
New factor New range
---------- = -----------
Old factor Old range
| Is This Answer Correct ? | 0 Yes | 2 No |
What is the differace between Volumatric flow meter and Mass flow meter.
Tr. Wiring for calibration.
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
How the flow can be measured by using DP Transmitter?
what is maximum temprature in instrumentation
dear friends pls tell me how temperature compensations are done in bourdoun tube of pressure guages thankx
where can we use viberation transmitter,and how can we control viberation?
Hello Friends do you know this answer of this Question? Which color you would use when there is Somthing not correct or need to change In P&ID? i mean color that use for highlight that need to update in P&ID. Yellow Highlighter ? Red color ? Blue Color ? Appreciate for your answer. Thanks Blue Color
how many types of orifice plates?and explain about it?
i want to Measure the Difference pressure of Packed distillation Column of height 3 mtr. h.p. side connected to bottom & L.P. side connected to the top , so tell me what will be THE URV & LRV of that D.P. transmitter?
can you give some devices that measure directly the mass flow rate.
how to do loop checking pls email to shanavaska2000@yahoo.com
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)