How the flow can be measured by using DP Transmitter?
Answers were Sorted based on User's Feedback
Answer / mobin ahmed sabayek
for flow measurment first need creat difrential pressur by
using of orific plat in flow path dp tranmitter have low
and high side cannect high pressure and cannect low side of
low presure of tapping and transmitter will convert
diffrential pressure in to 4 -20 ma
Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ashish namdev, bina refinery [
A DP type transmitter senses DP pressure from LP & HP tapping.
after sensing DP we will have to change some settings in the
transmitter, the settings are as follows -
1. set the range in output block.
2. change display parameter from linear to square root.
3. change display unit as per your requirement.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / george mathews
When we are going to measure the flow using a DP
Transmitter there must b a Flow Instrument placed there. So
if we see the basic structure of a flow instrument we can
clearly see that one side the orifice is normal and it goes
on shrinking toards the other end like a conical shape.
so we connect the higher end of the dp to the normal
orifice and the lower side to the other end of the flow
instrument. and when there is a flow there ll alwyas a
difference in the pressure as soon the water/ oil / gas
enter the flow instrument the normal end is at high
pressure but the exit end is at lower pressure due to d
manufacture of the instrument. And we can get out
measurment .
Is This Answer Correct ? | 1 Yes | 1 No |
what is the procedure to callibrate temp controller ,pressure controller,etc. suppose a temp controller showing error 1.5 degree centigrate how can i minimize it.
0 Answers Sabic, Saudi Aramco Shell Refinery Company SASREF,
with the help of suitable diagrams different types of control valves
Can we use PLC in Hazardous Area?
I have a close vessel tank which is under vaccum when in running condition so pl. Provide it's range for dp type tx whose flange to flange distance is 440 mm and density is 1
how to set calibration range in a DP transmitter to measure level for a closed tank and for an open tank,and also please explain me how to set calibration range for a DP flow transmitter in a line ?
why the output sugnal is 4-20 ma and not 4-25 ma?
How to Calibrate Radar Level Transmitter in Field
how to calibrate displacer type level transmitter by dry weight method please mention formula for weight calculation
Actual using of tube bender to bend 2 opposite 90 deg at correct measurement center to center of tubing.
What is shriking and swell effect for a boiler ?
Can we use thermocouple in generator of power station replace RTD(pt 100)? if we don't have any place for use RTD.
What are the two program execution modes of PLC?