How the flow can be measured by using DP Transmitter?
Answers were Sorted based on User's Feedback
Answer / mobin ahmed sabayek
for flow measurment first need creat difrential pressur by
using of orific plat in flow path dp tranmitter have low
and high side cannect high pressure and cannect low side of
low presure of tapping and transmitter will convert
diffrential pressure in to 4 -20 ma
| Is This Answer Correct ? | 7 Yes | 2 No |
Answer / ashish namdev, bina refinery [
A DP type transmitter senses DP pressure from LP & HP tapping.
after sensing DP we will have to change some settings in the
transmitter, the settings are as follows -
1. set the range in output block.
2. change display parameter from linear to square root.
3. change display unit as per your requirement.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / george mathews
When we are going to measure the flow using a DP
Transmitter there must b a Flow Instrument placed there. So
if we see the basic structure of a flow instrument we can
clearly see that one side the orifice is normal and it goes
on shrinking toards the other end like a conical shape.
so we connect the higher end of the dp to the normal
orifice and the lower side to the other end of the flow
instrument. and when there is a flow there ll alwyas a
difference in the pressure as soon the water/ oil / gas
enter the flow instrument the normal end is at high
pressure but the exit end is at lower pressure due to d
manufacture of the instrument. And we can get out
measurment .
| Is This Answer Correct ? | 1 Yes | 1 No |
What is ultrasonic flowmeter?
When a field input to plc is coming from 400 to 600 meters and the input is in 24 V DC? So signal cable of which cross section i should select for proper signal to plc?
how pressurize drum calibrated ?
What is the exact output of eddy current proximity probe? For vibration mesurment?
Why we use 250 ohm resister in series hart communicator?
I have a problem with a valve (air to close). When it is fully closed and try to open 1% it doesn't responce till 3% open suddenly more than 3% then back to 3%. I tried to tune positioner then removed it, the problem still exist. Any idea
How to gennerate earth leakage monitoring alarm for solenoid valves in control system?
how to calibrate absolute pressure transmitter
what is maxdna ?. explain about the software details.
Whether the DP transmitter can be utilised in the medium of Vaccum for the measurement of Level?
Hi, I'd like to know the purpose of MOS (maintenance override switch). At site, these switches are installed in a stanchion with the transmitter (connected to ESD). thank you.
3 Answers Adani, Adani Wilmar,
what is PM/CM/RCM?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)