Answer / rahul
For loop checking we are having ILD (instrument loop
drawings)as a documents. for AI we give 4-20ma and chek in
the system if accordingly raw count is coming or not.
for AO we force from the system and check in the plant if
according to raw count current is coming or not.
for ESD loop checking raw count in the system(Triconex) is
819 - 4095 i.e for 4-20ma
if there is problem is loops then we go for backward
checking i.e from system to know where is the problem.
then we do point to point checking.
after completion of loop test we go for functional test.
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / jeetu chaudhary
Half Loop Checks
A half loop check consists of a point to point wiring
check. Historically it is used to verify that by drawing
comparison, all of the wires are landed in the correct
spots.
Full Loop Check
The computer based documentation will verify that each
instrument that makes up the total loop is responding as
specified.
| Is This Answer Correct ? | 1 Yes | 0 No |
Why is the length of cable layyed from RTD to temp. Transmitter should be minimum? Why does heating effect takes place in their?
1 Answers Process Control Technologies,
what is the conductivity sensor output formula and what is the ph sensor output formula?
how to calibrate flow transmitter
In which principle Woodward Governor 505 work in power plant? What are the input of Woodward governor 505
What is rated capacity in Control valve
temptrure me ketne frequiency hote hai
What is the difference between PLC-HMI and DCS as each function of DCS based system is possible in PLC ?
Why we use 4 - 20 ma?
WHY RESISTANCE TEMPERATURE DETECTOR IS AN ACTIVE DEVICE
PLZ explain to me massflow
Draw a complete P&ID of a flow suction tank indicating all control & protection equipment. Indicate all its inlets and outlets. Explain the controls for this system
hello.my friends.i am an electronics & instrumentation engineer.i want to know Q1.why lugs use in instrumentation cable termination? Q2.if limit switch not working what to do?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)