how to find total current when kva is 30.4 given ? should we
use root 3 (1.732) in the formula?
Answers were Sorted based on User's Feedback
Answer / arumugam
can someone answer me the formulation how shri arrived the formula for A=kva*1000/(v*1.732.how does 1000 comes in formula. give me the formula.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shri..
KVA=30.4
Volt (LL)= 415
A= 30.4*1000/(415*1.732)
Per Phase Amps = 42.29
| Is This Answer Correct ? | 1 Yes | 2 No |
WHAT IS THE SETTING OF OVERLOAD RELAY AND UNDER VOLTAGE RELAY IN PERCENTAGE?
how to calculate the size of the cable for a particular rating 3phase induction motor?
1 Answers Godrej, Megatron Solutions,
what is the difference between squirrel cage & slip ring induction motor?
17 Answers College School Exams Tests, NTPC, Ramyaa Electro Gear,
What is Nominal voltage?
WHAT INSTRUMENT IS USED TO MEASURE THE MAGNETIC FLUX?
What is the effect on power factor, shown by a trivector meter; incase of reverse phase sequence. If the power factor of a system is lag what meter will show in case of reverse phase sequence connected to the meter. and What in case of lead.
A LT ckt i mean 440 volt flow of current100A.at this time HT current what will ON 11 KV &33 KV.plz givemy answer with example
what is vector surge & vector shift? we have 25.3 MW(11kv) generator & 11kv/132kv transformer, connected with with 132 kv grid.vector surge relay is tripping frequentaly.what is permissible maximum limit for this.
low voltage means how much voltage? extra low voltage means how much voltage? medium voltage means hos much voltage? high voltage means how much voltage? Ex: low voltage - 1volt to 240volt like this
Let's say I have 2 current carrying conductors C1 and C2 carrying currents of 5A and 10A. They are brought close to each other from a distance of infinity to a distance of 10cm away from each other - 1. What would be the values of current flowing in each conductor when (taking into account effects of interference of each conductor on the other) - a. The currents are AC b. The currents are DC c. C1 is AC and C2 is DC Please explain your answer with mathematical equations and formulas. Please specify the final numeric answer. Please make assumptions and clearly specify them.
if we know Fault level say 25 KA , How to decide busbar size for Distribution network of 1000 Amp Breaker ? Sample Calculation or Farmula Available or not ?
sir, Two different rating of generator going to connect parallel, can it set same DROOP or different. Why? Please explain
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)