sir,
Two different rating of generator going to connect
parallel, can it set same DROOP or different. Why? Please
explain
Answers were Sorted based on User's Feedback
Answer / sanu chaudhary
droop means speed regulation. if the machine is running at
1500 rpm at no load and the machine came on full load at
1545 rpm this means the droop of the governor is set 3%.so
if the both machine rating is equal hence droop should be
equaland if rating is diffrent ,droop should diffrent for
smooth operation of system .machine of higher rating should
have set less droop then other for equal load sharing
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / n.v.mani
Higher rated machine should be set at less droop than that
of lower rated machine,for equal load sharing and smooth
operation of system.If both machine ratings are equal,droop
should be equal.
Is This Answer Correct ? | 2 Yes | 1 No |
Could you measure voltage in series?
Why magnetic flux produces an induced current?? what is the detailed procedure ?? ans plz
What happened when we give 2 phase supply to a 1 phase equimpent. It's effect on equipment's efficiency and life?
in ACB breaker requireding 3200Amps. buscoupler getting OFF mode and again it reset and getting normal position give me a required answer?
What is a circuit breaker contact multiplier relay?
what is breaking capacity
there is an alternator 480 k.w, 400v,50hz, 4-wire running on load having leakage alternator body earthed current 38 A. is it within acceptable limit? if yes then give reference if no then how to bring within specified limit
How to take Vector group test of Transformer?
16 Answers Sunflag Steel, Zuari Cements,
how the transformer stables out zone faults? Because we use non directional O/C relays .Is there any special considerations are taking into account to overtake this?
what should be 3phase motor capacity or rating to connect in star connection. what should be 3phase motor capacity or rating to connect in delta connection. what should be 3phase motor capacity or rating to connect in star delta connection
Can the Neutral and Body Earthpits of a transformer conncted together by Earth strips under ground.
How can you calculate in detail the VA burden of current transformer used for Restricted earth fault protection? Please understand that the CT required here is Class PX or X. Also please show the calculations for knee point vtg, stabilizing resistor, magnetising current.