what is vector surge & vector shift? we have 25.3 MW(11kv)
generator & 11kv/132kv transformer, connected with with 132
kv grid.vector surge relay is tripping frequentaly.what is
permissible maximum limit for this.
Answers were Sorted based on User's Feedback
Answer / gobind
Whan the generator have synchronized with grid the waveform
have 120 Deg each phase but at the time of any fault
occurred in the grid system,at that time the waveform of the
grid voltage have been reduced from 120 Deg to min at that
time vector Shift Relay have operated.Permissible limit of
the vector Shift 8 Deg.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / ajay vikson
Hi,
here is a useful link on the vector surge relay
http://www.electrotechnik.net/2009/04/vector-surge-relay.html
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / k.p.sharma
We have the vector surge relay setting at 12 deg. But i observe that at that setting many time tg breaker tripped with grid breaker as per scheme only grid breaker trip is required. Please tell me is this setting ok or not.
K.P.Sharma
| Is This Answer Correct ? | 0 Yes | 0 No |
Dear all,recently in our plant we installed a conveyor for this the motor ratings are 5 hp and Amps 7.39.Due to on urgent starting of conveyor we fix the DOL starter with range of 9-15 amps.give me suggestion regarding on this issue
Why do you have to use Protecion relay with the function MTB ( Mechanical Trip Button ) for electrical system.
What is TR of AC?
If a manufacturer decribes a power supply transformer as providing a secondary voltage of 24 volts when connected to a 240 volts supply, do you think they are refering to the full load or no load secondary voltage?
What is the ladder circuit?
1 Answers Mitharg Information Systems,
what is difference between neutral and earth
Is an SCR semi controlled device?
Whats the purpose of neutral earthing?
5 Answers Electrical, Hindalco, TCS,
what is the clear formula to calculate cable size for a load
Why does the DC voltage needed is less than AC needed to produce corona?
How can we calculate strength of copper hich is supplying electric power to heater and in it hold the heater also and what r all types of forces which is acting on it...
How to checked frequency drive output voltages?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)