KVA transformer of different frequencies of
50hz,100hz,500hz&1000hz. which one of these transformer has
big size? Give reason
Answers were Sorted based on User's Feedback
Answer / vijendra joglekar
well transmission & distrubutions transformer(Electrical)
dosent decide by frequency normally it will comes as 50 hz
or 60hz depends upon country these transformers vary there
size by rating not by frequency .But in power electronics
transformers (Normally in Power electronics circuits for
example Switching on SCR HIGH frequency signal is required
were 500hz or more are used which is normally smaller size
but designed for very high frequency)
| Is This Answer Correct ? | 14 Yes | 5 No |
Answer / annarapu sairam
At higher frequencies the no of turns required is less so the
size of transformer is reducued.
| Is This Answer Correct ? | 5 Yes | 3 No |
In transformers back emf should be almost equal to the
applied voltage . For the same voltage ,less flux is
required at higher frequency. The core will be smaller ,and
hence the size
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / uma
inductive reactance is proportional to frequency and inductance. So for same inductance if frequency increases L can be decreased. where L is prop to volume. So higher the frequency lower the size required.
| Is This Answer Correct ? | 0 Yes | 1 No |
how much earth resistance consider to commissioning the transformer?
how to electronic energy metter failed in electomagnectic fild passing in the metter and which thing to defect more on metter.
calculation of knee point voltage of current transformer?
kindly send me 11KV MV motor differential protection procedure by primary injection method.
A transformer has negative voltage regulation when its load PF is A zero B unity C lagging D leading
What is the maximum percentage voltage drop (vd%)for a motor control center
why do you add the load short circuit impedance when considering short circuit amperage. It seems that you should only consider supply. If you need to consider loads and you don't know what loads are to be added , what would be a good sub-transient reactance rating for the loads?
What is the use of 1:1 isolation t/f in any circuit...?
How to calculate wire length,size & current? ( related to control panel)
0 Answers FSS, GK Controls, Panel Tech,
If a shunt Dynamo has induced emf 100V and 0.4 ohm resistance and battery of accumulator of open circuit emf 110V and 0.5 Ohm resistance are in parallel what is common terminal potential difference?
Triping principle of ELCB&RCCB? wht is the difference between these two?
Name the instruments which run on DC?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)