Answer / bibhas
ELCB is Earth leakage circuit breaker. It is very sensitive.
Even if there exists a minor leakage current, it will
immediately trip. Whereas RCCB is residual current circuit
breaker. It will trip only above the set trip value
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / k.prakashchandra
ELCB requires earth connection. Earth wire is taken through
ELCB to the body of the appliance.If there is any leakage
current in the earth wire ,it will trip.4 pole or 2 pole
RCCB requires neutral.It works on the principle that vector
sum of the currents in phases and neutral is zero or current
balancing.If there is any leakage current to the earth it
will be sensed by only phase and not the neutral resulting
in tripping.3 pole RCCB is for a 3 phase load without neutral.
| Is This Answer Correct ? | 1 Yes | 0 No |
hi, is there a difference in choosing bus bar for DC or AC ,,if there can anyone help me about. thanks
What is C curve and D curve of MCB?
What are the Steps for Testing of 20MVA (make:-CGL) Transformer? How many Test we have to do?
what is the resistance value of our human body?
Draw a 230kv two-bus bar system showing the following. 1.Two generators (150MW) each connected through one 15.75/230KV transformers 2. 1 outgoing lines 3. Two 230/130 KV transformers 4. BUS PT's 5. CT
what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx
How to configure the drives in PLC, through Profibus commnication. And to how to address it?
what is the difference between thermal magnetic release and microprocessor based release breakers. what are the advantages of latter over the first one...
5 Answers Jackson, Karthik Industries, McD BERL, TCS,
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
Define step response?
what is frequency? and its importance
how the speed decreases of a generator in power station if load increases
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)