What is the use of 1:1 isolation t/f in any circuit...?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi.
The main use of Isolation Transformer is to Isolate the
circuit without changing the voltage ratio. i.e. 1:1. It is
generally used in LT (415 V Three phase systems).
The isolation is needed because the LT system is much prone
to faults and the faults like line to ground faults are
common. At this level of voltage most of the petty but
important loads are connected. Human interface is maximum
and the system is not as Ingress protected as in case of HT
switchgear (Where seperate room and skilled persons only
have access). Therefore the fault level is dangerous and the
consequences can be even dangerous. Therefore to Reduce
fault level Firstly a transformer is inserted thus its
impedance %z comes into circuit (Series Impedance). And even
if fault occours you/ Device is isolated from the main
circuit which is actually feeding the fault. Thus it keeps
one safe and Protects severe damages that could have
happened otherwise.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
simply saying isolation of any circuit is used to isolate
from line to line line to ground and also for human shock
resist, because everyone did not know about the risk and
dangerous of electricity only skilled will know about it. so
every circuit is should be isolated for safer use
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / n k singh
The main use of isolation transformer is to isolate two
electrical circuits.
| Is This Answer Correct ? | 0 Yes | 0 No |
operation of protection relay watchdog contact?
explain why reduced voltage starters are required for large tree phase inudction motor
how to calculate the output power of vfd , please help me.
why did youi choose this career?
1 hp single phase motor is more likely to get hot thsn inone hp 3 phase motor its true or false? If true why?
what is the difference b/w pvc cu conductor and cu breaded wire..?
why contactors are used ...? is contactors and relays are same ...?
use of automatic voltage regulator & input voltage of it?
?? how to calculate lighting system ????
A synchronous machines has higher capacity for (1) Leading power factor (2) Lagging power factor (3) Does not depend upon the power factor of machine (4) None of the above
why we use primary delta connectin in hight voltage transformer
11 kv metering is done in my factory.Meter show PF 1.000 but kvarh lag&lead show 24&94 respectively & Avg.PF is .956 .? is what i do for inproove my PF to 1.000
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)