What is the use of 1:1 isolation t/f in any circuit...?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi.
The main use of Isolation Transformer is to Isolate the
circuit without changing the voltage ratio. i.e. 1:1. It is
generally used in LT (415 V Three phase systems).
The isolation is needed because the LT system is much prone
to faults and the faults like line to ground faults are
common. At this level of voltage most of the petty but
important loads are connected. Human interface is maximum
and the system is not as Ingress protected as in case of HT
switchgear (Where seperate room and skilled persons only
have access). Therefore the fault level is dangerous and the
consequences can be even dangerous. Therefore to Reduce
fault level Firstly a transformer is inserted thus its
impedance %z comes into circuit (Series Impedance). And even
if fault occours you/ Device is isolated from the main
circuit which is actually feeding the fault. Thus it keeps
one safe and Protects severe damages that could have
happened otherwise.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
simply saying isolation of any circuit is used to isolate
from line to line line to ground and also for human shock
resist, because everyone did not know about the risk and
dangerous of electricity only skilled will know about it. so
every circuit is should be isolated for safer use
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / n k singh
The main use of isolation transformer is to isolate two
electrical circuits.
| Is This Answer Correct ? | 0 Yes | 0 No |
29 Which of the following breaking method save energy? A regenerative breaking B plugging C dynamic breaking D none of above
should %impedance be high or low in a power transformer? if so why?
what is meant by earth fault and how it happens....
how we can calculate the efficiency of a diesel generator ?
Load 380kva eb 415v,load amps 350.Same load dg 415v,load amps 420 what reason ?
1 Answers AVT Natural Products,
Ash AAAC conductor is used for which KV lines
what happen if transformer neutral not earth
As a good company employee, can you report your supervisor to the company management if he or she is going against the company interest in his or her actions?
Why PT burnts?
a battery is having capacity 100AH and 25% charging .if a load taking 10A & connected 6 hour .what is the final condition of the battery.
why transformer ratings are in kva
How to test Power Transfomer vector group?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)