What is the use of 1:1 isolation t/f in any circuit...?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi.
The main use of Isolation Transformer is to Isolate the
circuit without changing the voltage ratio. i.e. 1:1. It is
generally used in LT (415 V Three phase systems).
The isolation is needed because the LT system is much prone
to faults and the faults like line to ground faults are
common. At this level of voltage most of the petty but
important loads are connected. Human interface is maximum
and the system is not as Ingress protected as in case of HT
switchgear (Where seperate room and skilled persons only
have access). Therefore the fault level is dangerous and the
consequences can be even dangerous. Therefore to Reduce
fault level Firstly a transformer is inserted thus its
impedance %z comes into circuit (Series Impedance). And even
if fault occours you/ Device is isolated from the main
circuit which is actually feeding the fault. Thus it keeps
one safe and Protects severe damages that could have
happened otherwise.
Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
simply saying isolation of any circuit is used to isolate
from line to line line to ground and also for human shock
resist, because everyone did not know about the risk and
dangerous of electricity only skilled will know about it. so
every circuit is should be isolated for safer use
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / n k singh
The main use of isolation transformer is to isolate two
electrical circuits.
Is This Answer Correct ? | 0 Yes | 0 No |
what is humming AC solenoid
how the global warming take place?
Why are transmission lines multiples of 11? Is it because of some historic reason ? Or is there a scientific base to it?
why can we use cosine wave instead of sine in ac supply as both have same rms vale and ripple factor
0 Answers Indcoil Transformers, Power Grid,
A jet of fluid strikes a plate What was the force required to counter it?
if there is nutral in phase why we use earthing wire and grounding? even at fault condition the fault current flows to neutral (it is a lower path)
hi frienda We have 750kva cater pillet dg set we are fasing one diffrent proublam in dg we are start dg set after one mint applying load around 450a load but dg was run 3 Or 4 mints after 3 mints dg was shuding down automatic how to face this proublam pls tel any budy
How can you calculate the size of the down conductor cable for the lightning protection system. Is 70mm2 cable can replace 95mm 2 bare copper cable when the copper tape size is 25Wx3 thk mm.
what is XF 200/240 V AC for Drawout Breaker.
What is emperical relation.Name few of them which are used in electriacl engineering?
What is Isolation Transformer???
which type of harmonics minimum produce in 12 pulse rectiformer transformer? a)3rd b)5th c)7th d)11th
4 Answers Power Grid, Powerica,