What is the use of 1:1 isolation t/f in any circuit...?
Answers were Sorted based on User's Feedback
Answer / aamod tripathi.
The main use of Isolation Transformer is to Isolate the
circuit without changing the voltage ratio. i.e. 1:1. It is
generally used in LT (415 V Three phase systems).
The isolation is needed because the LT system is much prone
to faults and the faults like line to ground faults are
common. At this level of voltage most of the petty but
important loads are connected. Human interface is maximum
and the system is not as Ingress protected as in case of HT
switchgear (Where seperate room and skilled persons only
have access). Therefore the fault level is dangerous and the
consequences can be even dangerous. Therefore to Reduce
fault level Firstly a transformer is inserted thus its
impedance %z comes into circuit (Series Impedance). And even
if fault occours you/ Device is isolated from the main
circuit which is actually feeding the fault. Thus it keeps
one safe and Protects severe damages that could have
happened otherwise.
| Is This Answer Correct ? | 10 Yes | 0 No |
Answer / bala
simply saying isolation of any circuit is used to isolate
from line to line line to ground and also for human shock
resist, because everyone did not know about the risk and
dangerous of electricity only skilled will know about it. so
every circuit is should be isolated for safer use
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / n k singh
The main use of isolation transformer is to isolate two
electrical circuits.
| Is This Answer Correct ? | 0 Yes | 0 No |
defult setting in p220 micom motor proction relay for 11kv,640kw,f.l.a.-40a,1440rpm ht motor?
why do we prefer -48 volt instead of -24volt or -12 volt etc. ??
in ct secondary one terminal is connected to earth why?
sir pls send the je exam - 2008 and other model question papers..
I have 500A load (WHICH IS SEPARATE MDP PANEL),an MCC panel with 4000A Breaker.Already I have 2500A load.Can I connect this load directly to the Busbar since I have PROTECTION IN MY MDP Panel ?
how to calculate overall efficiency of diesel generator set? give us a formula with an example.
why AC cannot to be stored and DC cannot be transmitted?
How do we check transformer losses and what are the ways to minimise it.
why only 26v dc is used in aircraft and 115v ac in aircraft.
HOW TO CALCULATE THE ILLUMINATION IN INDOOR LIGHTING?
in 220 kv substation,what is the mean of avr voltage reading? means at oltc temp. 36 the avr voltage was 109v.so what the mean of 109v
I am having a DG set.The 415 V from Generator is step up to 460 v and then the same is used for Induction furnace. before Step up, I am connecting LT load to my factory use. When Induction furnace is in service from DG, when i try to start a motor, the generator is tripped.Please tell me the reason.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)