what is the formula for backup time of online ups?
Answer / sudhakar g
Hi,
First you want to know how much required for your company or home anything.....suppose we can take 1200w load we required then take 1.5kva inverter
kw=kva x p.f
1200=kva x 0.8
kva=1500
number of SMF batteries=N=6
Voltage of each DC battery = V = 12 V
Ampere-hour of each battery (AH) = X1)
Suppose incase of 2hours usage T=2hours
Volt-Ampere = (N * V * X*EFFicency)/ T
1500 = (6*12*X*0.9)/2
1500 = 33X
X= 43 AH
or else
Time=(number of batteries*voltage of battery*AH)/VA
T=(6*12*43*0.9)/1500
T=1.9hrs
Nearly 100minutes
Is This Answer Correct ? | 7 Yes | 1 No |
how we have to calculate the short circuit current for 33/11kv 2mva, 7.5% Z, Transformer primary side breaker and secondary side breaker short circuit current for both sides?.
In a single phase converter, the no. of SCR conducting during overlap? a.1 b.2 c. 3 d. 4
How the value of KVAR of capacitor bank used in switchgears calculated??
IN electrical field, WHAT ALL THINGS THE CUSTOMER WILL ASK WHILE ORDERING FOR LT PANEL (ALL TYPES OF LOW TENSION PANEL)
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
How the earth fault relay works please explain?????????
Radio Carbon dating is used in a) find diseases b) find the age of relics c) find the carbon content in the atmosphere d) none of these
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
What is the basic working principle of Tri vector meter?
Why let through energy not considered for ACB breaker while cable sizing?
why doesnt the back emf hold the speed of unloaded series motor?
what is the working difference b/w softstarter and Variable frequency drive ?