only some transformers and some generator requires NGR why?
NGR - Neutral Grounding Resistor is used to limit the fault
current of a sytem.
So generally a system with high line voltage of 3.3KV and
above normally comprises of high load equipment which
results in very high fault currents due to a Short-circuit
fault. Normally during a Earth fault the fault current
flowing through the earthed phase is to be carried by the
remaining phases which may be very much more than the
rating of the conductors. So we follow the Neutral
Grounding practice so that the fault current is carried by
the nuetral.
Now this current carried by the nuetral is to be limited
such that this high fault current does not damage the
grounded equipment so in the neutral we insert a resistance
which is the NGR.
So for any high voltage system to limit the fault current
NGRs are used. for the equipment working at lesser voltage
normally can withstand the short circuit currents for short
time.
| Is This Answer Correct ? | 10 Yes | 0 No |
what is main purpose of ignator in halogen lamps.how to identify the failer of ignator in circuit
what is positive , negative & zero equivalent system resistance
what would happen if u assume to insulate all the overhead lines and no insulators....??do you think it to b an advantag or a disadvantage??justify.
What is the formula to calculate the rating of a three phase miniature circuit breaker
Please give the formula for converting from 1 tr refrigeration to kw.
what is difference between vcb and mccb
function of apfc pannel
i seen a 132kv/11kv transformer,and thier is a sugar factorys 10MW EXPORT PLANT,MY QUESTION IS THAT WHEN THEY EXPORT ELECTRICITY THEY USE THE SAME TRANSFORMER AND THE CONNECT IT TO 132/11KV TRANSFORMERS SECONDARY SIDE CAN ANY ONE EXPLAIN IT.. THE TRANSFORMER IS OF KIRLOSKAR MAKE AND IT HAS TAP CHANGER.
can i connect the two phases of scott connected transformer,if not why?
whatis the test procedure for lightning arrester which was installed one year back. i want check it whether it is working or not.
During underground cabling in landscape area what did we cover the cable with to prevent the electric shock & protect the cable?
what is the current limit of lighting arrester ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)