NGR - Neutral Grounding Resistor is used to limit the fault
current of a sytem.
So generally a system with high line voltage of 3.3KV and
above normally comprises of high load equipment which
results in very high fault currents due to a Short-circuit
fault. Normally during a Earth fault the fault current
flowing through the earthed phase is to be carried by the
remaining phases which may be very much more than the
rating of the conductors. So we follow the Neutral
Grounding practice so that the fault current is carried by
the nuetral.
Now this current carried by the nuetral is to be limited
such that this high fault current does not damage the
grounded equipment so in the neutral we insert a resistance
which is the NGR.
So for any high voltage system to limit the fault current
NGRs are used. for the equipment working at lesser voltage
normally can withstand the short circuit currents for short
time.
| Is This Answer Correct ? | 10 Yes | 0 No |
in our sub station why we step down firstly 33kv\11kv then 11kv to 430v. can we direct step down 33v to 430.v.
what is units of resistance
1.WHAT ARE TRANSMISSION LINE LOSSES DURING WINTER AND SUMMER SEASON? 2.WHAT ARE THE CAUSES/ 3.WHEN THE CORONA IS MORE?.,WHETHER WINTER OR SUMMER? 4. WHAT IS THE PERCENTAGE OF LOSSES IN TRANSMISSION LINE?
what is XF 200/240 V AC for Drawout Breaker.
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
Waht will happened if reactive power increase in the line? waht about active power increase too?
oltc of a transformer, how it works? and what are the equipment consist of describe briefly?
What is the difference between Earth and Neutral?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
Circuit diagram of tube light without starter using electrical choke
Wind mill
with 3 phase board on a 63 amp rcd is it ok to have 6 electrical showers 2 on each phase and what problems could happen
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)