Answer / k.prakashchandra
whenever a large load in the network is removed suddenly
there will be a swell in voltage due to reduction of IZ
drop.Rarely lightning strokes are also responsible for
this.And whenever there is a fault in the line ,it will
cause dip in voltage momentarily.
| Is This Answer Correct ? | 3 Yes | 2 No |
Answer / sdvyas,chartered engineer
Whenver any large inductive load like large rating motors
or capacitor bank is energised ,due to high inrush current
the voltage drop in the cable/line took place this result
into voltage dip in the system. Also, in case of fault in
electrical network the current shoot up extremely high and
voltage dip in the system may be noticed.
Voltage swell may be observed when inductive load on the
electrical network is suddenly thrown off as the energy
stored in the motor( inductive in nature ) can not last in
a very short time as the inductor takes times to last its
energy.In this situation 1/2 LISquare= 1/2 Cv Square and
voltage starts increasing. Other reason of voltage swell is
the lightening. During lightening, voltage induced in the
conductor may be superimosed on the power frequency and
this may lead to swell in voltage.
| Is This Answer Correct ? | 2 Yes | 2 No |
IN THE CASE OF AN ELCB, IF THERE IS ANY UNSTABILITY BETWEEN PHASE AND NEUTRAL IT MAY TRIP. BUT MY QUESTION IS WHEN A LOAD IS CONNECTED IN BETWEEN P AND N, THE LOAD CONSUMES SOME POWER AND THERE IS A DIFFERENCE IN NEUTRAL WITH RESPECT TO THE PHASE. THUS ACCORDING TO ME, THE ELCB WILL AUTOMATICALLY OPERATES WHEN EVER THE LOAD CONSUMES-- I KNOW IT IS WRONG. BUT THE SOLUTION IS?????????
why current flows from +ve to -ve terminal
What is SFU ?
aeroline vibration is present
comparision between ACB and VCB
what are the specifications for Dc cables of higher rating
What is the difference between LT CT & HT CT?Can we use indoor type transformer as an outdoor type or vice versa?
WHY THE +VE POLARITY OF 48V DC POWER SUPPLY IS USUALLY GROUNDED?
how can we can take BDV test in transformer?
What si the d/f b/w KVA & KWH, kvarh & kvar, kwh & kvar phase voltage & line voltage
what is CRGO Transformers?
6 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd, TATA,
Generally In transformer Tap Changer on HT side, but I have seen in 66KV side in 220/66 KV, 100 MVA, Areva make transformer. Why ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)