why we used for range in pnumatic 3-15 psi and current 4-20
ma?
Answers were Sorted based on User's Feedback
Answer / saravanamurthy
Hi,
4-20 mA standard is mainly to differentiate the conditions
live zero and dead zero i.e let me tell an example consider
a level sensor fixed in a tank . now the tank is empty .
then the sensor will send the reading as 0mA this zero is
live zero, if there is no standard as 4-20mA. in the same
case if there is any problem in the sensor output then also
the reading ll be 0mA this zero is Dead zero.In order to
differentiate the fault and the original process condition
we have chose this range as the standard.
Thanks & Regards,
S.I.Saravanamurthy.
Your comments are welcome
Is This Answer Correct ? | 101 Yes | 14 No |
Answer / pankaj kumar
because in b/n 3 to 15 psi the responce of actuator & control
valve is linear.before this hunting problem occurs.
we use 4 to 20 ma signal as standard signal because during
confurigation of hart 250ohm resistance or connected that is
easly converted in to voltage signal.(1v to 5v )......
instead of voltage signal current signal use because voltage
is pickup noise more as compare to current.
and in case of voltage signal chance of voltage
droff...............
Is This Answer Correct ? | 19 Yes | 5 No |
Answer / gunasekar.man
because it is use for voltage drop 4-20ma pnuematic input supply presure 6bar will be converted to be 3-15 psi are also its standrd use.some application will be use diffrent power supply for 5v,12v,24v.....but 4-20ma are constant
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / lomesh vadhankar
For 4-20mA, the linearity scale comes proper, as well as if
we want to convert, 4-20 mA than its easy to factorize, in
range of, 0-25%,25-50%,50-75% and 75-100%.. So, If suppose,
any control valve is needed to control, then it will be
easier to control it... And for other reasons, as
Mr.S.I.Saravanamurthy Perfectly said, is the ZERo zone. so
that, the Dead condition of any instrument can be
differentiated from normal Zero parameter condition.
Thank you..
Your comments are welcome
Lomesh Vadhankar
Is This Answer Correct ? | 10 Yes | 9 No |
Answer / saravanamurthy
Justification Steps:
1. Interpolate the coordinates of % opening and Current in Y-axis and X-axis Respectively
2.Connect the coordinates , you will get a straight line
3.Since it is with slope , it's our responsiblity to calculate the slope so that we can project it in normal plane
Slope Calculation:
a.Equation of straight line : Y=mX+C
where,
Y- Current in mA
X-%opening of full scale
m-Slope of the straight line
C- constant (calculated from Y intercept )
b.Calculate Slope using the formula:
m=(X2 - X1)/(Y2 - Y1 )
4.In this range of current , the value of slope is found to be constant , ie.m=0.16, but when we go for some other ranges slope changes as it ascends so its non linear for other ranges.
5.finally straight line equation for the above range is Y=0.16*X+4
6.This constant slope means that the line is linear
Regards,
S.I.Saravanamurthy
Is This Answer Correct ? | 4 Yes | 5 No |
Answer / biju antony
The transmitter output stance from what is known as "live zero". This system has
specific advantages :
1. The systems automatically alarms when the signal system becomes inoperative.
2. The output areas is linear ( Ratio of 1 : 5 ).
DEAD ZERO SIGNAL :
The advantage is that it does not have to be biased to true zero. A "Live zero" gives the
computer additional information, so that it can takes appropriate alarm action in case of a
measurement failure, because it can discriminate between a transmitter operating, but
transmitting a zero measurement and a failure, in the signal system.
Is This Answer Correct ? | 4 Yes | 6 No |
Answer / yashpal
i want to add just one thing that above mA there will be a
electromagnetic interference and signal may be distort due
to that.
Is This Answer Correct ? | 1 Yes | 4 No |
Answer / vivek jain
why not 0 to 3 mA becoz the output is nonlinear.(also live
zero(if it is a process variable)and dead zero(if there is
wire break))
4-20mA the output is linear.
also 20 is a multiple of 4 i.e why 20mA!
IF THE OUTPUT GOES ABOVE 20 mA THEN THERE IS UPPER LIMIT
VIOLATION I.E THE OUTPUT WILL REMAIN CONSTANT AT 20.5mA.
Is This Answer Correct ? | 1 Yes | 5 No |
Answer / rawjaw
Previous ans is right. But also
refer the answer posted by
others asked same question
by ONGC exams for the very
best answer
Is This Answer Correct ? | 1 Yes | 6 No |
Answer / mdshafiullakhan
why we should use for range in 3-15 psi and 4-20ma because
the linearity curve will starts from 4-20ma only during this
source range only we will get the linearised output that is
the reason and 0.22 psi to 1 kg the process will begins from
0.22 to 1 kg
Is This Answer Correct ? | 8 Yes | 23 No |
What is the procedure of changing a Faulty Module of Allen Bradley PlC without stopping the Process
we re giviang 24v supply to transmitter and we getting output from tx?now my question is wht we call this complete proces?
When we will do simulation for I/P?IF WE DO SIMULATION through which way either series or parallel?
What is modbus?
What is difference between ESD and PLC please Explain me clearly.
The performance of a pump is monitored by measuring the ________ and _________ pressures
How to Calibrate Vortex Flow transmitter in field
What is the difference between rich gas and lean gas?
how to calibrate temprature switch and flow switch ?
What is Vena contracta?
what is the diffirence between Earth and Neutral
What is surge and how is it prevented, what is the purpose of bypass valve across AS valve.