Can a pneumatic control valve work without positioner?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Yes, a pneumatic actuator can drive a valve without a
positioner.
In the HVAC world it's done all the time because the service
conditions (temperature/pressure/wear factor) for, say, a
chilled water valve does not necessarily demand the
precision control that a positioner offers.
An I/P (a current to pneumatic transducer) is used to
convert a 4-20mA control signal to a pressure control signal.
The service required in heavy process industries is usually
sever enough that a positioner is used on a control valve.
Company and industry practice will determine the use of a
positioner.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ajaya kumar behera
Yes we can only fully open/close by changing instrument air supply from header valve
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / tickno
yes it can ,but if the bench set of CV is on range 3-15 psi(instrument standadt unit,conversion from 4-20mA to 3-15 psi)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vergel
No, that is why i call a control valve, we need positioner to control the position of the actuator, if its a simple on off valve, no need for positioner...
| Is This Answer Correct ? | 1 Yes | 4 No |
What is motion balance principle?
what is vfd(variable frequency drive)?type of vfd.
which gas or which liquid is filled in capillary of dial type temperature indicators on power transformers
How to calibrate RC Feeder system in thermal power station?,If any instrument available to calibrate it,ple inform me. make:stock,
What is the absolute temperature
please tell no. & add. of consultancy who recruit me in power plant as instrumen engg. present i m working in power plant as ass.t instrument engg. thanku mahesh 09226562826
Why Flow measurement has to use Square Root
If relative y axis vibration sensor is by passed, and relative x axis and absolute sensor is left working. how much monitoring i would have risked?
how to callibrate a new i/p converter
what is easiest way to read STL language in PLC?
what is the input of digital counter during the the calibration time?
how u meassure room temp?is it possible 2 meassure room temp by rtd or thermocouple?between rtd n thrmocouple which is more regard?3 meassure diff. between rtd n thermocouple?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)