Can a pneumatic control valve work without positioner?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Yes, a pneumatic actuator can drive a valve without a
positioner.
In the HVAC world it's done all the time because the service
conditions (temperature/pressure/wear factor) for, say, a
chilled water valve does not necessarily demand the
precision control that a positioner offers.
An I/P (a current to pneumatic transducer) is used to
convert a 4-20mA control signal to a pressure control signal.
The service required in heavy process industries is usually
sever enough that a positioner is used on a control valve.
Company and industry practice will determine the use of a
positioner.
Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ajaya kumar behera
Yes we can only fully open/close by changing instrument air supply from header valve
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / tickno
yes it can ,but if the bench set of CV is on range 3-15 psi(instrument standadt unit,conversion from 4-20mA to 3-15 psi)
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vergel
No, that is why i call a control valve, we need positioner to control the position of the actuator, if its a simple on off valve, no need for positioner...
Is This Answer Correct ? | 1 Yes | 4 No |
what is DCS and SCADA?
Questions on flow meters,few questions on HART protocol,
What is Erosion in a control valve?
what is the difference between DELTA-V & FOUNDATION FIELD BUS
Can anybody tell which type of quections are asked in interview for projects? plz give its urgent.....!
who's take first position in process in the timing of new installation flow transmitter and control vavle. give the answer with logical trick.
Can Any body tell me how to check Modbus Settings in ER300N L&T trivector meter?
In instrumentation standard we use 4 to 20ma for transmission , why cant we use 3 to 19ma ?
how to calibrate temprature switch and flow switch ?
A flange is used for instrument connection for a system with a design temperature of 316C (600F) and a design pressure of 1000 kPa (145 psi). What is the class rating of the flange to be used for this application? Explain your answer
IF TX SHOWS SLOW RESPONSE, WHILE A CLOSE LOOP AND WHEN WE PUT THE CONTROLLER ON MANUAL THE PROBLEM RECTIFIED, SO WE CAN SAY THE PROBLEM IS IN
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows