Can a pneumatic control valve work without positioner?
Answers were Sorted based on User's Feedback
Answer / carl_ellis
Yes, a pneumatic actuator can drive a valve without a
positioner.
In the HVAC world it's done all the time because the service
conditions (temperature/pressure/wear factor) for, say, a
chilled water valve does not necessarily demand the
precision control that a positioner offers.
An I/P (a current to pneumatic transducer) is used to
convert a 4-20mA control signal to a pressure control signal.
The service required in heavy process industries is usually
sever enough that a positioner is used on a control valve.
Company and industry practice will determine the use of a
positioner.
| Is This Answer Correct ? | 5 Yes | 1 No |
Answer / ajaya kumar behera
Yes we can only fully open/close by changing instrument air supply from header valve
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / tickno
yes it can ,but if the bench set of CV is on range 3-15 psi(instrument standadt unit,conversion from 4-20mA to 3-15 psi)
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vergel
No, that is why i call a control valve, we need positioner to control the position of the actuator, if its a simple on off valve, no need for positioner...
| Is This Answer Correct ? | 1 Yes | 4 No |
plz tell me clearly about PID.."when v have to change I value,D value,GAIN??
Explain the difference between mmwc and mmwg?
what pressure transmitter?
what is hot loop check and cold loop check.
3 Answers Bapco Bahrain Petroleum Company,
i am confusing about differential pressure transmitter as i seen so many DPTs in different ranges how can we calculate level and flow with mmh20 plz tel me
which type of zones used for boiler? & why ?
DC motor and DC Drives working funda?
why we use 24 vdc in instruments mostly?
Dear friends, I have a question: We work on a project which has some boilers to provide steam for desalination unit. The boiler area is safe and the only hazard source is the fuel lines of boilers. I want to know according to NFPA standard which type of instrument should be selected on the fuel line: Eex Type or Non-Eex type? Thanks in advance
In control engg. : Differences b/w 1st order & 2nd order system, graphically & theoretically ?
I have one DP transmitter of range 0-500mmWC i have to calculate its range in M3/hr for flow measurement so whats the formula.
Draw a P& ID showing – orifice flange, plate, dp transmitter, isolation & bypass valves and tubing.
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)