Why starters are using the machines???
Answers were Sorted based on User's Feedback
Answer / deepak24
starter are used because of the following reason-
1. to start and stop motor
2. for protection (short circuit protection, open circuit protection, thermal protection, over voltage etc.)
3. to improve starting torque of motor
4. to limit the starting torque
| Is This Answer Correct ? | 13 Yes | 1 No |
Answer / nishwa
stat and stop operation,
to limit the starting current(star delta starter),
over load current and fault current and shot circuits current that current sense by relay,
variable speed operation
| Is This Answer Correct ? | 9 Yes | 1 No |
Answer / sainianil
starter is mainly used for the protection of machine and we with the help of starter we can able to isolate the machine from the main power supply in case of fault ,
the following items used in starter are:-
1 isolator: to cut the main supply to the machine without effecting the system
2 fuse: for shortcircuit protection
3relay for the overcurrent
4 contactor controlled by the control ckt
now a days it is replaced by the MCB because of its longlife..{FOR SHORT CKT AND OVERCURRENT}
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / nupurpatel
To start and stop the motor,
To limit the starting current,
To limit the high starting torque.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / pitchi reddy
To limit the starting current and to protect machine for high currents
| Is This Answer Correct ? | 0 Yes | 3 No |
ho w to make Incident and accident reporting
IS THE ANY DIFFERENCE B/W GENERATORS & ALTERNATORS
What is the difference between the watt hour meter and Var hour meter in terms of internal connection and work theory . ie "When the meter records watt-hour an when the meter records var hours ??"
Conventionally, capacitors are considered to generate reactive power and inductors to consume it,how??????
what is the reason for choosing DYn11 in transformer, why not DYn12 or something else
State thevenin’s theorem?
for 100 HP Induction motor service factor is 1.2(SF) we placed a VFD at the motor side load is balance with 0.3 Amp's Phase to Phase but at incoming of VFD load is un-balance with 10 to 20 Amp's what will be cause of load un balance
how to calculate of which rating transformer should be selected? take any example
how external lighting design? please give examples?
What mean 150 amp hour write on battery.
what is the purpose of supervision relay coil
what is meant by armature reaction & where its happen ?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)