What is 100%
protection of
generator? Why
95% protection
is used not 100%?

Answers were Sorted based on User's Feedback



What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / aswin joseph

95% stator earth fault protection uses an overvoltage relay at the neutral transformer of a generator. Because there is always a minimum voltage at the neutral because of harmonics and zero sequence, a little margin is necessary and only 95% of the generator windings can be covered with this method.
100% stator earth fault protection uses current injection at low frequency or minimum third harmonic voltage to detect earth faults. It does not have the limitation at the earth side of the winding, so using this method and the one described for the 95% you can cover 100% of the stator.
Both detect earth faults at generator stator windings when generators neutrals are connected to earth using neutral transformers or reactance, which make neutral currents too small to use overcurrent relays.
Injection method protects 100% stator windings without the need of a 95% relay. It works on its own.
The principle is the following: a signal generator injects voltage pulses in the windings of the machine at a frequency different from the rate frequency of the system or any harmonic (typically 10 Hz to 25 Hz, 87 Hz...). These pulses are transmitted to ground through the winding insulation and back to the signal generator through the earthing resistor.
Together with the signal generator, the relay also measures the current in the signal injected. In normal conditions, total impedance is high and low currents are measured. If there is a phase to earth fault in any phase, impedance to ground decreases and current increases rapidly, indicating the fault.
This method works even with the machine out of service if the relay is connected (careful with this during maintenance).
This system is normally implemented at the generator neutral transformer, but if it is not available (for example, because a resistance or reactance is used instead of a transformer, or the generator is delta connected), voltage transformers can be connected at the generator terminals with the secondary connected in broken delta, since this allows the injection of the same signal to all windings.

Is This Answer Correct ?    32 Yes 7 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / shailesh tankni

generators are basically synchronizing machine if a fault
occurs, they fall out of synchronization. but if the fault
is temporary or for a very small duration micro seconds or
seconds then the alternator/ generator may again achieve
synchronization without permanent interruption of supply.
this is the reason why the 95% protection is provided
instead of 100% protection.

otherwise for even for the small fault we would experience a
cut off eg: a small fault like contact of two phase
conductors due to sudden wind. which is a temporary fault.

Is This Answer Correct ?    42 Yes 36 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dayanidhikinkar

since few turns of wdg have very small voltage therefore
fault current flowing through secondary of CT is less than
preset value for relay operation.Hence relay will not
operate for that much portion of winding.

Is This Answer Correct ?    11 Yes 8 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / m bhargava narayana

for 0-95% stator earth fault over voltage relay is used,where as 95-100% earth fault(because small amount of third harmonic zero phase seq currents flow through neutral induces small voltage at neutral) under voltage relay is used.

Is This Answer Correct ?    1 Yes 1 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dr. s.r.krishnamurthy

If a fault occurs at say 98%th portion of generator phase
winding reconed from the phase terminal, the voltage
induced in that balance 2% winding is not sufficient to
drinve a fault current through the differential relay.
Hence intentionally 100% protection relay is not used.

Is This Answer Correct ?    2 Yes 8 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / sandip upare

Generator having lot of protections rotar-stator wdg. earth
fault,over voltage,over current etc.
For that each relay having setting from 0-100 per. with
time period in seconds
According to type of fault we have to set the setting

example :- for earth fault protection we have set upto 50-
70per. because if we set to 100% every and each small
leakage relay trip

so my thinking is only that the setting of each protection
is depend up application of DG only on what load

Is This Answer Correct ?    18 Yes 25 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / vijaybharadwaj202

to provide the 100% protection for alternator ,it interrupts
the operation of generation even low level faults, so we can
provide protection for alternator 95% instead of 100%

Is This Answer Correct ?    5 Yes 13 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / rohit singh

Because in the case of Generator if we choose the 100%
protection then the protection system cost more than the
generator cost. thats why we will choose 95% of protection.

In India generally 92-93% protection is used whereas inother
country it is 95-96%.

Is This Answer Correct ?    5 Yes 16 No

What is 100% protection of generator? Why 95% protection is used not 100%?..

Answer / dalveer

BECAUSE IF WE USE 100% PROTECTION FOR THE GENERATORS THEN
IT CAN'T BE WORK PROPERLY. IF ANYONE HAVE ANY DOUBTS THEN
CALL ME...... 09729722179

Is This Answer Correct ?    3 Yes 70 No

Post New Answer

More Electrical Engineering Interview Questions

What are the causes of eddy current losses?

1 Answers   Schneider,


how to find the voltage's of a transmission line plzz help with pictures i am not able to understand

0 Answers   Student,


what are the major & minor faults that occur in an inverter and in UPS ? And how to repair and resolve them ?

0 Answers  


cable armor

3 Answers  


How we can calculate the life of Lead acid battery

0 Answers   ABC,






What is essential to prove safe isolation of electrical circuit?

0 Answers  


Why IGBT is very popular nowadays?

3 Answers   TVS,


We are dealer in Maharashtra State & We have recd. form C from dealer of Maharashtra State against our E-1 form. Now assessing authority is asking for counterfoil of our E-1 form. But, our E-1 form counterfoil is misplaced somewhere & assessing authority is disallowing the C form which is recd. from Maharashtra State.Please let us know the option for allowing C form?

1 Answers  


how to find out difference between ELCB, MCB and RCB on looking on it

1 Answers  


the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?

0 Answers  


What are the different methods for calculating Short Circuit Curren?

3 Answers  


how wud i know that whether i have to use unitized package substation or transformer?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)