what happen "when Dyn11 is parallel operation with Dyn1"?
Answers were Sorted based on User's Feedback
Answer / akhilesh singh
Due to 60deg phasor diff., PD of two secondaries will
arise. Therefor a circulating current between these two
secondary flows which causes shortcircuiting.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / dubai
I agree with murali.
Transformer having -30˚ angle (here DYn 11) can be
paralleled with +30˚ (here DYn 1) angle by reversing the
phase sequence of both primary & secondary terminals of one
of the transformers eliminating phase angle errors.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / thatharao
Both the terminals will reverse and Phase displacement will
be zero.So phase angle will be zero.
| Is This Answer Correct ? | 1 Yes | 0 No |
here phase difference between to secondaries will be 60deg
transformers belonging to dy1 could be operated in parallel
with those of dy11 or viceversa by transposing two of
external high voltage connections of one of the
transformers and also corresponding low voltage external
connections .it is not necessary to change any internal
connections
| Is This Answer Correct ? | 9 Yes | 13 No |
Answer / ramniveth and subuhani
same pottential of two neutral cannot be earthed .because
it give rise to third harmonics.so it cannot be paralleled
| Is This Answer Correct ? | 7 Yes | 11 No |
how Local Breaker Backup relay working?
In Star type and Delta type Motors, If one phase will miss/Break then which phase winding will burn and why?
Why reactive power is needed in a power system? How is it being absorbed or delivered by alternators? For reactive power control we are changing excitation but reactive power absorbing or delivering related to stator. How these two are interlinked? i want a detailed explanation with necessary expressions and figures?
what is the full form of MEMO? name of memo train.
need of capacitor used in plant
In our homes we place the 5Amps fuse...now in our house only takes 5Amps for all normal conditions ha???
why is the earthing pin on 3 pin top are big and thick
can anyone give an idea about dia calculation in cold rolling mill
how to select the no. of brushes in a lap winding?
Brief working principle of fluorcent tubelight,function of starter & choke.
How does frequency affect KVA rating of a transformer? If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz frequency then how will its KVA rating change? a-increase b-decrease c-remains same Also explain why do u think like that.
WHY TRANSFORMERS ARE RATED IN 11KV 22KV 33KV Instead off 10kv 20kv 30kv
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)