what is effect of reverse c.t connection on metering.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
No effect on ammeter.In EM type Watt meter and energy meter
the readings reversed.In ETVM import and export interchange.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / vels
one phase is reversed then the Energy meter will not give correct reading
but 3 phases are reversed then the current direction shown are wrong and the reading of MW ,MVAR are showing import instead of export
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sureshkumar
incase protcetion CT not protective the equipment, so direction is must.
| Is This Answer Correct ? | 1 Yes | 0 No |
Can u explain : how capacitor act when the supply is given is a.c and d.c. I know that when d.c supply is given then the capacitor charges and becomes open circuited. But please say about when a.c is given. I have seen that when a.c supply is given ,it charges and discharges, But when we plug in capacitor to our daily supply and take it out ,then we join those wires spark will appear,which seems charge is present ,but when a.c is given it should charge and discharge
redundant connection in contactor?
during the period of armature reaction ,if the brush shift is not accomplish, what happen?
what does the transformer connection symbol YNaod1 mean ?
How to calculate no of Lighning arrestors are required for protecting 50mX 50m*20m cubical building and locations of LA?
what is the vvvf in the dumbwaiter?? or lift. what is the actual process?/
in case of OC+EF relay, how the burden is divided/calculated/shared by the CTs in case of normal (healthy condition) and during fault conditions.? three coils of OC & ef coil is conected in residual connection across the three CTS.
What are the advantages and disadvantages of open loop control system?
In IDMT RELAY the term minimum (M) indicates what?
why did lightening arrester rod probe sharp?
how to check the continuity of a cable with a megger
I have 11KV/415V power distribution transformer. I have found unbalance current in LT (415V) side. Also observed that unbalance voltage (3V) at LV side due to HV side unbalance voltage. What should I check for this? Also, the same LV side load can run in balance on captive power.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)