what is effect of reverse c.t connection on metering.
Answers were Sorted based on User's Feedback
Answer / k.prakashchandra
No effect on ammeter.In EM type Watt meter and energy meter
the readings reversed.In ETVM import and export interchange.
Is This Answer Correct ? | 6 Yes | 1 No |
Answer / vels
one phase is reversed then the Energy meter will not give correct reading
but 3 phases are reversed then the current direction shown are wrong and the reading of MW ,MVAR are showing import instead of export
Is This Answer Correct ? | 3 Yes | 1 No |
Answer / sureshkumar
incase protcetion CT not protective the equipment, so direction is must.
Is This Answer Correct ? | 1 Yes | 0 No |
differentiate between one way two gang switch & two way one gang switch, used in designing the loads of building.
what do w do when the output of generator is fluctuating?
What is the most accurate way of testing ELCB?ELCB is better than RCD?
how to select short circuit current while selecting a MCCB? how to calculate current for a given KVA and KW load?
2 Answers GE, PnU Engineering,
HOW DO WE COLLECT THE SOLAR ENERGY AND DESCRIBE THE METHODS TO CONVERT THE SOLAR ENERGY INTO ELECTRICAL ENERGY?
11/.433KV, 100KVA TRANSFORMER is supplied with .433KV AT ITS PRIMARY. HOW MUCH KVA IT CAN SUPPLY
Why transformer called by KVA?
in 11kv generators the neutral point is connected to earth via earth coil while in the 33 / 11 kv transformer the neutral point is connected to earth via earth resistor why?
what is REF relay?
What is the main difference between power transformer and Distribution transformer?
9 Answers APTransco, Bhel, NTPC,
If i have 200 test cases and we have to execute but we don't have time to execute all testcases.within 1 hour we have to execute that testcases and prepare the test report.so how i have to resolve this problem? is there is any technique in the testing.
Is only insulation the difference between High voltage and Medium voltage cable?