In Transformer testing at Shop test we normally test for
vector group, open ckt.,short ckt. but what are the other
test performed for transformer once it reaches at site.For
e.g:if the transformer is dry having rating 1000KVA?

Answers were Sorted based on User's Feedback



In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but wha..

Answer / guest


1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits

Is This Answer Correct ?    2 Yes 0 No

In Transformer testing at Shop test we normally test for vector group, open ckt.,short ckt. but wha..

Answer / brahma

Also Double voltage double frequency, if customer ask impulse

Is This Answer Correct ?    0 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

I need HT sphere gap calibration table. Can any body help me.

0 Answers  


what is the setting of locked rotor in HT motor ? (answer expecting in percentage)

0 Answers  


How PSV sizing being done

0 Answers  


In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.

0 Answers   Hyatt,


What is the difference between vector surge relay (78) and Pole slip relay (98G)

0 Answers  






what is the tolerance for the magnetic balance test conducted on the distribution transformer?

0 Answers  


A 10 kva ,400v/200V , single phase transformer with 10% leakage impedance draws a steady short -circuit line current of

1 Answers  


What is maximum demand and contract demand?

5 Answers  


what is phase angle ? and also tells me why my phase-phase voltages are 390 rather then my single phase voltages are 221 and 223 respectivly?

2 Answers  


how to amps calculate from 1KVA?

11 Answers  


method to check earthing

5 Answers   ECC,


Why tripping not occur when the transmission breaks? Doesn't we provide earthfault protection for it?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4452)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)