In Transformer testing at Shop test we normally test for
vector group, open ckt.,short ckt. but what are the other
test performed for transformer once it reaches at site.For
e.g:if the transformer is dry having rating 1000KVA?
Answers were Sorted based on User's Feedback
Answer / guest
1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brahma
Also Double voltage double frequency, if customer ask impulse
Is This Answer Correct ? | 0 Yes | 0 No |
I need HT sphere gap calibration table. Can any body help me.
what is the setting of locked rotor in HT motor ? (answer expecting in percentage)
How PSV sizing being done
In diesel generator how AVR get voltage to excitation. And basic diagram DG EXCITATION CIRCUIT.
What is the difference between vector surge relay (78) and Pole slip relay (98G)
what is the tolerance for the magnetic balance test conducted on the distribution transformer?
A 10 kva ,400v/200V , single phase transformer with 10% leakage impedance draws a steady short -circuit line current of
What is maximum demand and contract demand?
what is phase angle ? and also tells me why my phase-phase voltages are 390 rather then my single phase voltages are 221 and 223 respectivly?
how to amps calculate from 1KVA?
method to check earthing
Why tripping not occur when the transmission breaks? Doesn't we provide earthfault protection for it?