In Transformer testing at Shop test we normally test for
vector group, open ckt.,short ckt. but what are the other
test performed for transformer once it reaches at site.For
e.g:if the transformer is dry having rating 1000KVA?
Answers were Sorted based on User's Feedback
Answer / guest
1. Insulation Resistance Measurement
a . For LT systems, use only 500V or 1000V Megger
b. For MV & HV systems, use 2500V or 5000V Megger
c. Remove Earth from Transformer neutral
2. Winding Resistance Measurement
R-N AND r-n
Y-N y-n
B-N b-n
3. Magnetic Current Test
Applied Voltage : RY YB BR
Measured Current : R Y B
4. Magnetic Balance Test
5. Vector Group Confirmation.
6 . Short Circuit Test and Differential Stability.
7 . REF Stability Test
8. Cooler Circuits.
9. Auxilliary Protection Circuits
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / brahma
Also Double voltage double frequency, if customer ask impulse
Is This Answer Correct ? | 0 Yes | 0 No |
If we have a 2000kva load,How much kvar capacitors we go to add to improve the power factor at 0.9?pls give the calculation and fully theory?
What are the types of relay ?
the current which flows during lightening is ac or dc,,,,,,,,,,, WHY
how to reduce shorting current in a slipring induction motor
what is relation between torque and speed / rpm?
How to identify phases in the transformer like motor and AC generator but one condition without phase indication like(RYB,UVW)?
What is clock position of Transformer?what are the clock positions are there?and what is different of them?
how can we calculate the current
can anyone give an idea about dia calculation in cold rolling mill
which strater used genearalyy???and why???
How power is transferred from one winding to another in an auto-transformer? A) electrically B) magnetically C( both a & b D) neither of above
Why material of brush is carbon in motors why not other material.