there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
Answers were Sorted based on User's Feedback
Answer / guest
Dear P.Kalivada 100KVA transformers total power (3 phase) is 100KUA one phase give 33KVA, Phase voltag is 11/1.732 = 6351 volt therefore current is 33000/6351=5.1 amp (at unit pf). You can see a name plate of 100KUA 11KV/433v tranrsformer it is written 5 amp as HT Current and 133 amp as LT side current you can verify any tranformer whose primary voltage is 11KV it's current is approximately to #/20 and secondary side of 433V it's current is approxhmately to # +#/3 ( # is how much KVA)
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / guest
HT side current = #/20 LT side current =#+#/3 ie 100KVA 11KV/440V transformer it's HT side current = 100/20=5 amps LT side current=100+100/3=133 amps. this is approximatelly figure(answer), Line man of Power Distribution Company fallow this method .
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / sunit
this is simple .. assume a 100kva tr, ok
then p= vi ( power = voltage x current)
1.lets see for HT side
p( kva)= root 3 ( for 3 phase)x voltagex current
=> kva = root3xvxI
=> 100kva=1.732x11kvxI
=> I= 5.25amp/phase
2. similarly in secondary side means LT side
=> 100kva=1.732x440xI
=> I= 144amp/phase
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / zaman
5KW capacity motor stare connection 410 volt pf 1 current 7.5 amp how mouch current carry of delta connection
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant kalivada
KVA = KV x A
= voltage in KV x current in ampere
So, A = KVA / KV at HT side
therefore if KVA is 100 and KV is 11 then
A= 100 / 11
= 9.09 Amps at HT side
and for LT
A = KVA / (V/1000)
= 100 / (440/1000)
= 100 / 0.440
= 227.27 for LT side
| Is This Answer Correct ? | 6 Yes | 10 No |
what happend to DC shunt motor if its field winding insulation becomes slightly weak? will that motor can run on full load or not explain in detail. thanks
can we measure +,-.zero sequence current ....? if so how can ???
Why earthing is necessary for any equipment?
We have ONLINE UPS 15KvA (3PHASE 440V I/P,3PHASE O/P,440V) I want to step down from 440 to 220 V What to do. Pl. suggest with specification.
Alternators are invariably star connected why?
At full load wat is the motor p.f And at no load will is the motor p.f?
in electrical control panel. how can i choose the cable rating. (example - 11kw motor, 18-25A mpcb}
What are the saftey parameters in transformers?
How to Prepare preventive maintenance shedule of machine tool.
what is the speed of electricity?
The magnitude of sum of two sinusoidal av voltage is equal to 230 volt.the magnitude of each individual voltage is also equal to 230 volt.what must be the phase difference between voltages?
0 Answers PGVCL Paschim Gujarat Vij Company Limited,
Do you know how to measure the earth resistance? if so explain it
42 Answers ABB, BEL, BridgeStone, College School Exams Tests, Dalkia, Dalmia Group, DEC, Electrical, Genpact, HEC, IOCL, JLL, L&T, MSEB, Saraca, Sical, Telecommunications, University Exams,
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)