there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
Answers were Sorted based on User's Feedback
Answer / guest
Dear P.Kalivada 100KVA transformers total power (3 phase) is 100KUA one phase give 33KVA, Phase voltag is 11/1.732 = 6351 volt therefore current is 33000/6351=5.1 amp (at unit pf). You can see a name plate of 100KUA 11KV/433v tranrsformer it is written 5 amp as HT Current and 133 amp as LT side current you can verify any tranformer whose primary voltage is 11KV it's current is approximately to #/20 and secondary side of 433V it's current is approxhmately to # +#/3 ( # is how much KVA)
| Is This Answer Correct ? | 17 Yes | 5 No |
Answer / guest
HT side current = #/20 LT side current =#+#/3 ie 100KVA 11KV/440V transformer it's HT side current = 100/20=5 amps LT side current=100+100/3=133 amps. this is approximatelly figure(answer), Line man of Power Distribution Company fallow this method .
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / sunit
this is simple .. assume a 100kva tr, ok
then p= vi ( power = voltage x current)
1.lets see for HT side
p( kva)= root 3 ( for 3 phase)x voltagex current
=> kva = root3xvxI
=> 100kva=1.732x11kvxI
=> I= 5.25amp/phase
2. similarly in secondary side means LT side
=> 100kva=1.732x440xI
=> I= 144amp/phase
| Is This Answer Correct ? | 8 Yes | 6 No |
Answer / zaman
5KW capacity motor stare connection 410 volt pf 1 current 7.5 amp how mouch current carry of delta connection
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / prashant kalivada
KVA = KV x A
= voltage in KV x current in ampere
So, A = KVA / KV at HT side
therefore if KVA is 100 and KV is 11 then
A= 100 / 11
= 9.09 Amps at HT side
and for LT
A = KVA / (V/1000)
= 100 / (440/1000)
= 100 / 0.440
= 227.27 for LT side
| Is This Answer Correct ? | 6 Yes | 10 No |
what do you mean by switchgears?
5 Answers Practical Viva Questions,
what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?
WHY WE ARE EXPRESSING KW-HR AS UNIT OF ELECTRICITY.........?WE CAN EXPRESS IN ANOTHER UNIT.....?
what happens if DC earthing and AC earthings are shorted?
why it is not advisable to run low rating (19KVA) DG sets in parallel for long durations even though they are provided with droop ckts (QDC)
Can the efficiency of transformer be measured with the help of wattmeter readings taken at primary and secondary side? Support the answer.
i have been tasked with a design of protection, metering and control(PMC) relay panel extension to accommodate all PMC relays.There is an already existing panel where this one will be built.What are the design aspects for this kind of project? thank you.
What is spike & surge.
What is multiplying factor of meter if the meter ctr and ptr is open type?
What happens if there is no nuetral in the power system?
What do you mean by Stimulastion Test in Diesel Genarator / Why & when it's conducted ?
How do you connect the capacitors on polyphase circuits?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)