there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.
Answer Posted / prashant kalivada
KVA = KV x A
= voltage in KV x current in ampere
So, A = KVA / KV at HT side
therefore if KVA is 100 and KV is 11 then
A= 100 / 11
= 9.09 Amps at HT side
and for LT
A = KVA / (V/1000)
= 100 / (440/1000)
= 100 / 0.440
= 227.27 for LT side
| Is This Answer Correct ? | 6 Yes | 10 No |
Post New Answer View All Answers
i need project topics along with circuit diagram in the electrical and electronics engg and also some websites regarding projets.
regarding safety what would u consider the most important rules to observe when inspecting electrical equipment?
why the pf of semiconductor device is improved the electrical devices
How to select circuit breakers rating eg. if i select a circuit breakers of capacity 40 amps DC with operating voltage 28 volts and if i what to use same circuit breakers for 300 Volts DC application what is the current rating of this circuit breakers.
What is a parabolic signal?
What is the actual meaning of thermal power efficiency ?
How to set the relay,,??
what is vA rating and class of a ct.
What is the method to solve circuit using source transformation?
What are the classifications of heating element?
1.main parts of generator? what is used A-check,B-check,C- check? 2.what is FM200 system in data centers? 3.difference between pac,ahu?
1.what is difference between ATS & STS main use. 2.what is difference between ACB& VCB With symobles,and main partes, manimum range. 3.How many types of relays and main function.
How can eliminate noise problem inside temperature controller temp. variation due to contactor chattering problem.
What are motor generator sets and explain the different ways the motor generator set can be used ?
what is advertised hop count