Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...

there is a # KVA Transformer of 11 KV/440V, in simple(not use formuia) how can you calculate it's HT & LT side current.

Answer Posted / guest

HT side current = #/20 LT side current =#+#/3 ie 100KVA 11KV/440V transformer it's HT side current = 100/20=5 amps LT side current=100+100/3=133 amps. this is approximatelly figure(answer), Line man of Power Distribution Company fallow this method .

Is This Answer Correct ?    8 Yes 6 No



Post New Answer       View All Answers


Please Help Members By Posting Answers For Below Questions

what is the purpose of shading ring or shading coil in electrical equipments.

4484


What is I to C?

2160


Is it good to short Neutral and Ground in the PLC or DCS main Power supply. Pls give YES or NO with reasons...? Simarpreet

2546


how to select diiferent power transformers of same capacity on no load loss and full load loss by economical point of view.?

1979


How each of the following losses occur in d.c machines (i) copper (2)core (3) windage (4)friction please help me

2042


what is plunger and what's the use of it in motor alignment?

2652


What is the meaning of loop in transformer

1808


why single CT used in DOL starter power circuit?

2533


What is Instantaneous Earth fault relay,how will work

2244


What happens if the series current double?

1483


How many energy meters can be connected on a 15VA Voltage transformer. please send a calculation sheet.

1949


how synchronous condenser is used in place of synchronous generator with out negotiating IEEE standards? Can i use 3 generators as synchronous generators and 2 generators as a synchronous condensers in an IEEE 14 bus system with out disturbing the standards?

2135


In Designing the rating & accessories of a MCCB how to choose the type of releases..means what is the basis for selecting, thermal magnetic, electromagnetic & microprocessr based releases

2030


HOW TO CALCULATE HV CABLE SIZING?

3228


What is MSL designation of a motor and same may be provided in details.

1723