why farmers are use earthing instead of neutral for their light conec. at
field.is it safe
Answers were Sorted based on User's Feedback
As there is a vast difference between the Earth & Neutral
The ground or "earth" wire is a circuit's safety protective
wire that normally carries no current.
It is there to force a fuse to blow or a circuit breaker or
GFCI to trip if a fault condition occurs in any appliances,
their flexible cords or plugs that are connected into the
circuit.
By carrying away the excess current in a fault condition -
which should cause the protecting fuse to blow or circuit
breaker to trip - the "ground" or "earth" wire protects the
building and its occupants because the power should be cut
off before anyone gets electrocuted or any overloaded
circuit wiring or appliances catch on fire.
The neutral is the normal "return" wire: in systems where
the load is supplied from only one hot (or "live") wire, the
neutral completes the circuit and carries current back from
the load to the power station.
All the neutral and ground (or "earth") wires in a building
are tied or linked together at the incoming service main
breaker panel. This is the only place they should ever be
tied together because it is "upstream" of all the fuses
and/or circuit breakers protecting the hot (or "live") wires
for the various circuits installed in the building.
Warning: we must never assume that a neutral is safe to
touch: it has to be checked with a voltmeter or a voltage
indicator to be sure it is not "live". This is because a
neutral wire is designed to carry current under normal
circumstances.
So, if a neutral wire going back to the incoming main
breaker panel has not been properly connected - or suffers a
deliberate disconnection or some accidental damage which
causes it to break - then it and any neutral wires connected
to it further downstream will go live up to the break
because of being connected to the downstream loads which
still have hot feeds coming into them!
That is why we should never use a neutral as a substitute
for a proper, separate, ground or "earth" wire.
| Is This Answer Correct ? | 2 Yes | 1 No |
1.wat is the advantage of induction motor? 2.wat is diffrence between 1-phase and 3-phase induction motor?
Which type of drive is advantageous AC or DC and why?
Hello Friends, How can we recognize the CT Star Point is S1 or S2 in case of Electro Mechanical Relays and what is meant by Restraining coil in relays and what is the purpose of that.. thank you in advance..
In case of power/distribution transformer what is percent impedence?
without any theoretical calculations, can u approximately tell the current rating of a motor(above 30hp)working at 415VAC.
what is mean by transition resistance of transformer?
what is the effect of vector group while phase sequence of a generator changes,whether the vector group changes or not
CAN 50Hz transformer work at 60 Hz power supply? if yes how it is possible?
what is induction furnance? how many phase supply given io its coil for 15 or 20 ton furnance?
Explain the operation of damper winding
Write down the name of 2 lady Bir Pratin of Bangladesh
What core magnetic balance test of transformer? How to do this test in a three phase Star delta (star-LV, Delta-HV) transformer? How to measure and where to measure? thanks and regards Austin
22 Answers Neutech, Power Grid, TSSPDCL,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)