Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


why farmers are use earthing instead of neutral for their light conec. at
field.is it safe

Answers were Sorted based on User's Feedback



why farmers are use earthing instead of neutral for their light conec. at field.is it safe..

Answer / rk

As there is a vast difference between the Earth & Neutral
The ground or "earth" wire is a circuit's safety protective
wire that normally carries no current.

It is there to force a fuse to blow or a circuit breaker or
GFCI to trip if a fault condition occurs in any appliances,
their flexible cords or plugs that are connected into the
circuit.

By carrying away the excess current in a fault condition -
which should cause the protecting fuse to blow or circuit
breaker to trip - the "ground" or "earth" wire protects the
building and its occupants because the power should be cut
off before anyone gets electrocuted or any overloaded
circuit wiring or appliances catch on fire.

The neutral is the normal "return" wire: in systems where
the load is supplied from only one hot (or "live") wire, the
neutral completes the circuit and carries current back from
the load to the power station.

All the neutral and ground (or "earth") wires in a building
are tied or linked together at the incoming service main
breaker panel. This is the only place they should ever be
tied together because it is "upstream" of all the fuses
and/or circuit breakers protecting the hot (or "live") wires
for the various circuits installed in the building.

Warning: we must never assume that a neutral is safe to
touch: it has to be checked with a voltmeter or a voltage
indicator to be sure it is not "live". This is because a
neutral wire is designed to carry current under normal
circumstances.

So, if a neutral wire going back to the incoming main
breaker panel has not been properly connected - or suffers a
deliberate disconnection or some accidental damage which
causes it to break - then it and any neutral wires connected
to it further downstream will go live up to the break
because of being connected to the downstream loads which
still have hot feeds coming into them!

That is why we should never use a neutral as a substitute
for a proper, separate, ground or "earth" wire.

Is This Answer Correct ?    2 Yes 1 No

why farmers are use earthing instead of neutral for their light conec. at field.is it safe..

Answer / anil

anil

Is This Answer Correct ?    0 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

Conventionally, capacitors are considered to generate reactive power and inductors to consume it,how??????

1 Answers  


how to calulate bearing number of any motor ?

0 Answers   Transfield,


Up to how much limit of HP of electric motor the Star- Delta Starter can be used ?

1 Answers  


The screw thread commonly used for transmission of motion is one of the following types of threads

0 Answers   Caterpillar,


why we use REF and Differential Protection in one transformers?my doubt is both protections are operated in internal fault only.why we want to use 2 protections?please clarify.

7 Answers  


wat is the need of capacitor on aceiling fan?

5 Answers  


Why is it prefer to initiate circuit breaker failure by "86" lockout relay not by "94" tripping relay ?!

0 Answers   OEG,


How can we calculate the transformer rating if the load calculated is 1000KW (11Kv Supply)?

0 Answers  


what is the formula for calculating of dielectric strength of transformer oil.

2 Answers   Bhel,


What is Avg. Power Consumption of 2 TR Split A/C???How v can calc. this???

1 Answers   Emerson,


generaly all power generating devices is expressed in KVA or MVA then why power ststion is expressed in MW

6 Answers  


Hi,iam a diploma in electrical engineering.rtd from indian air force in apr 2007.prsently working in reliance next link as a network maintenance engineer since 2007,can i get a job in motherson sumi.

0 Answers   Motherson, Motherson Molds and Diecasting Ltd.,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)