why farmers are use earthing instead of neutral for their light conec. at
field.is it safe
Answers were Sorted based on User's Feedback
As there is a vast difference between the Earth & Neutral
The ground or "earth" wire is a circuit's safety protective
wire that normally carries no current.
It is there to force a fuse to blow or a circuit breaker or
GFCI to trip if a fault condition occurs in any appliances,
their flexible cords or plugs that are connected into the
circuit.
By carrying away the excess current in a fault condition -
which should cause the protecting fuse to blow or circuit
breaker to trip - the "ground" or "earth" wire protects the
building and its occupants because the power should be cut
off before anyone gets electrocuted or any overloaded
circuit wiring or appliances catch on fire.
The neutral is the normal "return" wire: in systems where
the load is supplied from only one hot (or "live") wire, the
neutral completes the circuit and carries current back from
the load to the power station.
All the neutral and ground (or "earth") wires in a building
are tied or linked together at the incoming service main
breaker panel. This is the only place they should ever be
tied together because it is "upstream" of all the fuses
and/or circuit breakers protecting the hot (or "live") wires
for the various circuits installed in the building.
Warning: we must never assume that a neutral is safe to
touch: it has to be checked with a voltmeter or a voltage
indicator to be sure it is not "live". This is because a
neutral wire is designed to carry current under normal
circumstances.
So, if a neutral wire going back to the incoming main
breaker panel has not been properly connected - or suffers a
deliberate disconnection or some accidental damage which
causes it to break - then it and any neutral wires connected
to it further downstream will go live up to the break
because of being connected to the downstream loads which
still have hot feeds coming into them!
That is why we should never use a neutral as a substitute
for a proper, separate, ground or "earth" wire.
| Is This Answer Correct ? | 2 Yes | 1 No |
what is transformar load balancing ?
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
why lightining is not available in swith yards?
what is IP 55 & IP 54 ?
what is transformer tap change HT side and LT side
What is RTCC in a transfomer and specify its function.
Hi My Dear All Friends, There is one question it is widely used in Power Project's High Voltage Engineering. Question- What is the diffrence between Earth fault and Back up Earth Fault....???? . . . . . . Have A Good Day
A 400KVA transformer has 400 Hz frequency. If the frequency is changed to 50 Hz, then what will be the new KVA rating?
what is called star connection and delta connection also purpose of this connections?
what will happen if the secondary of current transformer kept open....
Difference between SFU & FSU with advantantages & drawback?
Frequency of rotor emf in induction motor is around A same as stator frequency B 50% C 5 % or below D 30%
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)