Frequency of rotor emf in induction motor is around
A same as stator frequency B 50%
C 5 % or below D 30%
Answer / anas feroz
Rotor emf is induced at slip frequency.
Rated slip ranges from 2% to 5% in normal induction motor's and can be as low as
0.5% in heavy induction motors to reduce the losses.
Hence rotor emf frequency will be s*Fs where
Fs= stator frequency.
| Is This Answer Correct ? | 0 Yes | 0 No |
1. The DC generaror,s induced output emf is connected with a DC motor(as load). when increasing the load of the motor by using brake drum or any way. what are the parameters will changes in both motor and generator(voltage, current, resistance, frequency, speed, torque, power, flux etc...) 2. Similarly for AC generator and AC motor 3. similarly if using DC batteries instead of DC generator, What happens?
What is the name of powder which is used in inner side of a cable? and purpose?
I COMPLITED MY B.TECH AND 10TH CLASS WITH 70%MARKS BUT 12TH CLASS 55%MARKS..CAN I GET INDIAN RAILWAY RECUREMENT EXAMINATION?
11. As per the theory current doesn’t flows in Neutral, but practically it is not applicable, explain why? 12. How to take the Vector Group Test in Transformer? What is the purpose of doing Vector Group Test? 13. Why the transmission lines are in 11kV, 22kV, 33kv, and why not 10kV, 20kV, 30kV? 14. Why do we generate 3 Phase AC Supply? It is possible to generate 4 Phase and 5 Phase explain it? 15. Explain why the Voltage drop will happen in 3 Phase line? 16. What is the equipment used to control the generator output? 17. What are the factors to be considered during the Synchronization? 18. What should be value of Circuit breaker operating time and tripping time? 19. Why the CT Secondary is rated as 5A generally? 20. At which time Synchronous generator act as a Synchronous Condenser?
Why we use the D-curve MCBs in critical power distrubution.
Dear all i want to know FEWA Electrical Supervisor Licence test Previous Year Questions ? If any body know please send to me shibin_75@yahoo.com
what do you mean by synchronous speed of a three phase induction motor?
In Air circuit breaker LSIG protection unit is used. Without fault in cables (2 runs 3Cx150Sq.mm Copper, 1Kv grade, XPLE armored cable IR value is more than 550Mohm @ 500V Megger) and load section Long time Overcurrent protection is triggers and trips the unit. We changed LSIG protection with new factory tested unit. Even then fault is persisting. Please suggest the possible causes
How to calculate KW what is the formula for KW.
The iron loss in a 100kva transformer is 1 kw and full load copper losses are 2 kw, then what is maximum efficiency occure at a load?
how can i reduce sparking without stepdowning the voltage
How to assume answer to electrical questions
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)